PostPosted: Tue Feb 09, 2016 10:44 pm
How can I achieve delay(wait_ time in Structure Text code?
Thanks,
PostPosted: Wed Feb 10, 2016 1:02 am
You need to use a TON function block and either an IF statement or a CASE statement, depending on the need complexity.
For a very basic solution:
   Delay : TON;
   Count : INT := 0;
Delay(IN:=TRUE, PT:=T#1S);
IF NOT(Delay.Q) THEN
   RETURN;
Delay(IN:=FALSE);
//delay is over.... More code here
Count := Count +1;
This is a simple example. Be sure to call the TON FB with FALSE once to reset it so it is ready for the next time... This example should result in the variable Count incrementing roughly every second.
In real life, you probably need something more advanced, but it hopefully helps you out.
Note: code above was manually typed in - I may have a typo or two
Scott Cunningham
KEB America, Inc.
www.kebblog.com
www.kebamerica.com
PostPosted: Sun Feb 14, 2016 10:34 pm
in this function block you can use a input var for the time.
shooter@home.nl
computer shooter
paul deelen
jacob van wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
skype shooter paul.deelen
phone +31736139136
PostPosted: Wed Feb 17, 2016 10:07 pm
Thanks for the reply guys,
I tried to duplicate your code, please tell me why the code below is not working. Only the first timer is working not the second one.
a:=1;
b:=2;
c:=3;
wait5(IN:=TRUE, PT:=T#5S);
IF NOT (wait5.Q) THEN
RETURN;
wait5(IN:=FALSE);
a:=7;
b:=8;
c:=9;
wait6(IN:=TRUE, PT:=T#5S);
IF NOT (wait6.Q) THEN
RETURN;
wait6(IN:=FALSE);
PostPosted: Thu Feb 18, 2016 1:55 am
In your program, wait6 timer is only reached when wait5 timer expires. Look at the flow of your code - if wait5 timer is not finished, then return - so the rest of your code is skipped. You only need multiple timers if you need to run timers simultaneously.
Your code must run every PLC scan - it's not like a PC script - you don't go from the first line to the last line and then be "done". Every PLC scan (xxx uS), your code is run. If you need to do steps 1,2,3, then you need a state machine (CASE statement):
CASE Step OF
   0: //init
      Step := Step + 1;
   1: //first timer routine
      a := 1;
      b := 2;
      c := 3;
      wait(IN:=TRUE, PT:=T#5s);
      IF wait.Q THEN
         wait(IN:=FALSE);
         Step := Step + 1;
   2: //second timer routine
      a := 4;
      b := 5;
      c := 6;
      wait(IN:=TRUE, PT:=T#15s);
      IF wait.Q THEN
         wait(IN:=FALSE);
         Step := Step + 1;
   3: //done - don't do anything more
   ELSE //code error!!! restart state machine
      Step := 0;
END_CASE
Now your code executes this way:
  • PLC scan 1 - case 0 executes (step incremented)
  • PLC scan 2 - case 1 executes (timer starts - 5 seconds)
  • PLC scan 3 - case 1 executes (timer running)
  • PLC scan 4 - case 1 executes (timer running)
  • PLC scan xx - case 1 executes (timer expires, timer disabled, step incremented)
  • PLC scan xx+1 - case 2 executes (timer starts - 15 seconds)
I hope that helps!
Scott Cunningham
KEB America, Inc.
www.kebblog.com
www.kebamerica.com
PostPosted: Thu Feb 18, 2016 2:57 pm
To scott_cunningham,
It helped a lot, can't thank you enough.
Thanks again.
:D
PostPosted: Sun Mar 25, 2018 8:36 pm
Hello !
I have tried the similar logic and it's not working. I developed a Functional block called "Fan_VFD" and used in a Program "PRG" of CFC type. Everytime when Fan_enable is TRUE;VFD_enable and error_VFD are FALSE, the timer has to count 10sec and execute the following steps. But it isn't happening in this case. The output of the timer is not resetting to False when IN:=FALSE. Please help me resetting the timer.
[code][/code]
FUNCTION_BLOCK PUBLIC Fan_VFD
VAR_INPUT
diff_pres:REAL;
VFD_cal_setpoint:REAL;
VFD_enable:BOOL;
Fan_enable:BOOL;
error_VFD:BOOL;
bypassTimer:TON;
VAR_OUTPUT
VFD_setValue:WORD;
VFD_status: BOOL;
Fan_status: BOOL;
VAR_IN_OUT
isolator_status:BOOL;
byPass_status:BOOL;
IF Fan_enable AND NOT VFD_enable AND NOT error_VFD THEN
isolator_status:=FALSE;
bypassTimer(IN:=TRUE, PT:=T#10s);
IF bypassTimer.Q THEN
bypassTimer.IN:=FALSE;
VFD_status:=FALSE;VFD_setValue:=0; bypass_status:=TRUE; Fan_status:=TRUE;
PostPosted: Wed Mar 28, 2018 3:24 am
You need to call the timer function block to get it to work and update the output variables. If you look at your code, you only call the function block inside of an IF/THEN block.
The difference is that your code simply set the input variable to false, but did not execute the function block. You need to do every scan if you want the timer to run:
bypassTimer();
Scott Cunningham
KEB America, Inc.
www.kebblog.com