Hi,

We're currently in the process of trying to port our existing PLC into the CoDeSys environment. Our machines have several access doors, therefore we're instantiating 4 instances of Door_POU.

That is fine but there are times during developement when one of the doors isn't working correctly and we'd like to see why. When I log into the runtime and double click on the POU the help manager window appears and lists all the instances and the implementation. I can open for example the 3rd instance but I cannot set any breakpoints within it. I can however open up the IMPLEMENTATION and set breakpoints within that. This "implementation" code appears to represent the first instance which does not help if my problem is only experianced by the 3rd instance.

I guess in my mind this seems wrong for two reasons. The implementation window should just contain the code like it would if you were logged out and editing. It isn't an instance. The instances should be able to have breakpoints set as they are actually being executed.

What are your thoughts ?

Thanks,
Michael.


Top
   
PostPosted: Fri Apr 01, 2005 2:38 pm 
Offline
Site Admin
User avatar

Joined: Mon Jan 31, 2005 10:48 am
Posts: 237
You are right:
Breakpoints in FB instances is a feature that is missing. And it will not be supported in CoDeSys V. 2.3. But 3S will implement breakpoints in FB instances in CoDeSys 3.0, which will be released at the end of 2005.

But there is a workaround you could use:
Define one more input variable in the implementation (a dummy variable), e.g. a boolean variable and initialise it whith TRUE when calling the FB instance from your main POU. In the FB code you insert a conditional operation, e.g. something (in ST) like

IF DUMMY THEN
DUMMY := FALSE;
END_IF

and position your breakpoint to the code line with the assignment. In the other IEC languages you can solve the same by using the operator MOVE and an additional EN (enable) input (e.g. in LD or CFC).

I hope this will help you to debug the problem. Of course you should remove the additional code after you have found the bug.

_________________
Roland Wagner
Moderator


Top
   
 Post subject:
PostPosted: Mon Apr 04, 2005 12:15 am 
Offline

Joined: Fri Apr 01, 2005 12:07 am
Posts: 8
oh ok, yep that works. I haddn't thought of doing that. Thanks !


Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 3 posts ] 

All times are UTC+01:00


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Limited