online communication with PLC using CAN interface

fleaplc
2020-01-17
2020-01-20
  • fleaplc

    fleaplc - 2020-01-17

    I need to connect to an Epec controller with CAn interface (I have Kvaser USB-CAn adapter installed in my PC) but I cannot find the way to set can interface into communication settings..

    IMG: CODESYS_570sWfZ9jE.png

     
  • sgronchi - 2020-01-17

    Hi fleaplc, could you please share which Epec device you are using?

     
  • fleaplc

    fleaplc - 2020-01-18

    I'm using 6200 series ECU

     
  • sgronchi - 2020-01-20

    You normally connect to the 6200 via Ethernet 1, not via CANbus*. Out of the box it has IP address 192.168.0.2.
    See section "Getting started" -> "Going online and downloading application" of Epec Programming and Libraries Manual, and "Programming" -> "Programming 6000/X Series Units" -> "Configuration" -> "Configuring Ethernet and DNS Settings".
    If it is already programmed, you can use CANmoon to connect to it.

    *I think you could use also the CAN gateway, but it is slower than Ethernet: you can find instructions again in "Going online and downloading application".

     