Multiple connections to CoDeSysOPC-Server
2019-06-13
2019-09-01
  • edmorrissey - 2019-06-13
    We are currently trying to connect the OSIsoft PI System to a CoDeSysOPC-Server using the PI OPC DA interface.
    There is also an Stange ECS application connected to this CoDeSysOPC-Server.
    When the Stange ECS application is connected to the CoDeSysOPC-Server, we are unable to connect with the PI system.
    Has anyone experienced something like this or would have any suggestions for me?
  • eschwellinger
    eschwellinger - 2019-06-21
    sounds like the max Client is exeeded ( Default is 4)
    If i understand it, you do not get values from the CODESYS PI to your OPC DA server connected Client, right?
    You could extend the Client by adding to the
    /etc/CODESYSControl_User.cfg
    [CmpChannelServer]Buffersize=1600000MaxChannels=8
    do not forget to restart the Pi after this change.
  • e.kislov - 2019-06-21
    Edwin, can you explain "Buffersize=1600000"? What the buffer, which dimension of value (bytes?).
    "Channel" represents only CODESYS OPC connection to PLC? Or any connection like IDE connection, web-visu connection, etc.
  • eschwellinger
    eschwellinger - 2019-06-22
    BUFFERSIZE is the overall amount of memory to be used by all channels
    MAXCHANNELS defines the number of channels that may be handled
    Β concurrently.
    Since each channel needs separate send and receive channels
    the available communication buffer is BUFFERSIZE / (2*MAXCHANNELS)
    - Webvisu
    - OPC UA
    - OPC DA
    - CODESYS
    each occupy one channel...
  • e.kislov - 2019-06-22
    Thank you for explanations.
  • edmorrissey - 2019-06-28
    Hi Edwin
    Thanks for your response. I have searched the etc folder an it does not contain the config file or any files from CODESYS.
    Could you please tell me where exactly I can locate this file?
    Regards
    Ed
  • eschwellinger
    eschwellinger - 2019-09-01
    which version do you have installed on the PI?
    (CODESYS runtime 3.5.x.x)