Welcome to our new forum
All users of the legacy CODESYS Forums, please create a new account at account.codesys.com. But make sure to use the same E-Mail address as in the old Forum. Then your posts will be matched. Close

SoftMotion SMC_ERROR.SMC_DI_HWLIMITS_EXCEEDED

smb2700
2018-06-30
2018-07-03
  • smb2700 - 2018-06-30

    Hi,
    I have a problem with the use of a new servomotor and drive, with a 20 bit encoder if I try to move the motor with MC_MoveRelative I have the following error: SMC_ERROR.SMC_DI_HWLIMITS_EXCEEDED.
    I try to check on the help but is missing.
    With other drive + servos I do not have these problems.

    Currently I installed:
    - CODESYS V3.5 SP12 Patch 1
    - CODESYS SoftMotion 4.3.1.0
    - CODESYS Control for BeagleBone SL

    Attached the image with the error.
    How can I solve the problem ??
    Am I wrong or is it a bug?

    Thank you

    IMG: Errore.png

     
  • alwoso - 2018-07-02

    Hi smb2700!

    Did you check the drive settings? Does the drive itself give a fault message, too?
    If there is no fault on the drive, check the PDO-mapping - maybe there is a mismatch between the drive's mapping and the mapping in your program....

    Good luck!

    Alfred

     
  • smb2700 - 2018-07-03

    Hi Alfred,
    the problem was in the setting of digital inputs. I remaped inserting them, and this led me to error. Since I have not yet connected my proximity switches to do these tests, I have inverted the status of the inputs on the drive, and it works.

     

Log in to post a comment.