Hi,
I am having a problem with the codesys service. Indeed, after several hours of operation, the automat stops and I can not know why.
I have not made any changes and the program has been running for 2 years now.
when I make the command "ps aux". I see that the service is stopped.I have to do "sudo service codesyscontrol start" and it starts again.Someone can tell me how to diagnose this?
I am in Wheezy.Codesys V3.5.11.20 and I made the latest wheezy updates.
thank you in advance
Ludovic
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
you could relicense with the CMLicenseNew.WibuCmRaU file..
see the FAQ's.
User the CODESYS file browser to save the CMLicenseNew.WibuCmRaU to your pc
and then reativate it.
(Before you do this... clean up the content cmact_license Directory - means delete the content) and restart the PI plc...
Then reactivate by this file.
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi ,
My file is 116.1 kb and I see that it must be between 130 and 140 kb.
Confirm that my file is empty?
I do not have a backup. Is there a way to recover the license otherwise?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
this 'manipulation' is the recommended 'retore the license' procedure,
I would recommend to prefer to use it in compare to the using of the 'tar' file method.
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I am not sure if I had the exact same problem, but my visualisation also stopped working after 8 hours or so, giving
me the VisuFctCheckForUnusedClients error (Removing Client at address xxx), and Channel closed because unused for 60s.
This Raspberry had already been Licensed!
What seemed to be the problem, whas that the operating mode in codesys was still switched to debug mode.
In the taskbar at the top of Codesys, go to: Online --> Operating Mode --> Select "Operational"
Not 100% sure that this is the reason why I got the same error message, and my Visu Crashing after 8 hours, but it seems to
be running fine now for the last 12 hours..
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
you need to add logfiles ...
cat /tmp/codesyscontrol.log
then we could check.
If it is really urgend sure it is aleways possible to use a support ticket.
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
I am having a problem with the codesys service. Indeed, after several hours of operation, the automat stops and I can not know why.
I have not made any changes and the program has been running for 2 years now.
when I make the command "ps aux". I see that the service is stopped.I have to do "sudo service codesyscontrol start" and it starts again.Someone can tell me how to diagnose this?
I am in Wheezy.Codesys V3.5.11.20 and I made the latest wheezy updates.
thank you in advance
Ludovic
Hi,
could you please Login by ssh and the execute a:
cat /tmp/codesyscontrol.log
BR
Edwin
Hi,
Here's what I find:
pi@raspberry ~ $ cat /tmp/codesyscontrol.log
(0021);*********
;<loggername>/tmp/codesyscontrol.log</loggername>
;<logoptions>
; <enable>1</enable>
; <type>normal</type>
; <timestamp>rtc</timestamp>
; <deactivatable>0</deactivatable>
; <dump>always</dump>
; <filter>0x0000000f<filter>
; <maxentries>1000</maxentries>
; <maxfiles>1</maxfiles>
; <maxfilesize>1000000</maxfilesize>
;</filter></filter></logoptions>
;<entries>
;Timestamp, CmpId, ClassId, ErrorId, InfoId, InfoText
;</entries>
;*********
1514495832, 0x00000013, 1, 0, 0, <logoptions>
1514495832, 0x00000013, 1, 0, 0, <benable>1</benable>
1514495832, 0x00000013, 1, 0, 0, <type>normal</type>
1514495832, 0x00000013, 1, 0, 0, <timestamp>rtc</timestamp>
1514495832, 0x00000013, 1, 0, 0, <disableable>0</disableable>
1514495832, 0x00000013, 1, 0, 0, <filter>0x0000000f<filter>
1514495832, 0x00000013, 1, 0, 0, <maxentries>1000</maxentries>
1514495832, 0x00000013, 1, 0, 0, <maxfiles>1</maxfiles>
1514495832, 0x00000013, 1, 0, 0, <maxfilesize>1000000</maxfilesize>
1514495832, 0x00000013, 1, 0, 0, </filter></filter></logoptions>
1514495832, 0x00000001, 1, 0, 4, CODESYS Control V3
1514495832, 0x00000001, 1, 0, 5, Copyright (c) 3S - Smart Software Solutions GmbH
1514495832, 0x00000001, 1, 0, 6, <version>3.5.11.20</version> <builddate>Sep 15 2017</builddate>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>CM</cmp>, <id>0x00000001</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>CmpMemPool</cmp>, <id>0x0000001e</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>CmpLog</cmp>, <id>0x00000013</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>CmpSettings</cmp>, <id>0x0000001a</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysFile</cmp>, <id>0x00000104</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysTimer</cmp>, <id>0x00000116</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysTimeRtc</cmp>, <id>0x00000127</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysTime</cmp>, <id>0x00000115</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysTask</cmp>, <id>0x00000114</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysTarget</cmp>, <id>0x00000112</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysSocket</cmp>, <id>0x00000111</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysShm</cmp>, <id>0x00000110</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysSemProcess</cmp>, <id>0x00000119</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysSemCount</cmp>, <id>0x00000139</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysSem</cmp>, <id>0x0000010f</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysReadWriteLock</cmp>, <id>0x0000013e</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysProcess</cmp>, <id>0x0000010e</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysOut</cmp>, <id>0x0000010b</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysMutex</cmp>, <id>0x0000013a</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysMsgQ</cmp>, <id>0x0000010a</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysModule</cmp>, <id>0x00000109</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysMem</cmp>, <id>0x00000108</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysInternalLib</cmp>, <id>0x00000107</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>_</cmp>, <id>0x00000103</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysEvent</cmp>, <id>0x00000102</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysEthernet</cmp>, <id>0x0000011c</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysDir</cmp>, <id>0x0000011b</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysCpuHandling</cmp>, <id>0x00000101</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, System: <cmp>SysCom</cmp>, <id>0x00000100</id> <ver>3.5.11.10</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpWebServerHandlerV3</cmp>, <id>0x00000072</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpWebServer</cmp>, <id>0x00000071</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpVisuServer</cmp>, <id>0x00000057</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpVisuHandler</cmp>, <id>0x00000054</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpUserMgr</cmp>, <id>0x00000061</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpUserDB</cmp>, <id>0x00000064</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpTraceMgr</cmp>, <id>0x00000070</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpSrv</cmp>, <id>0x0000001c</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpSocketCanDrv</cmp>, <id>0x00005f0d</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpSchedule</cmp>, <id>0x00000019</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpRouter</cmp>, <id>0x00000018</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpRetain</cmp>, <id>0x00000017</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpRasPi</cmp>, <id>0x00000089</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpPlcShell</cmp>, <id>0x00000128</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpOpenSSL</cmp>, <id>0x00000033</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAStack</cmp>, <id>0x0000008d</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAServer</cmp>, <id>0x00000124</id> <ver>3.5.11.10</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAProviderIecVarAccess</cmp>, <id>0x00000126</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceServer</cmp>, <id>0x00000016</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClientIec</cmp>, <id>0x0000011d</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClient</cmp>, <id>0x00000015</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpMonitor2</cmp>, <id>0x00000032</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpIoMgr</cmp>, <id>0x00000012</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpIoDrvIec</cmp>, <id>0x0000005a</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpIecVarAccess</cmp>, <id>0x00000060</id> <ver>3.5.11.10</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpIecTask</cmp>, <id>0x00000011</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpIecStringUtils</cmp>, <id>0x0000007f</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpGwCommDrvTcp</cmp>, <id>0x00000010</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpGateway</cmp>, <id>0x0000000f</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpFileTransfer</cmp>, <id>0x0000005e</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpEventMgr</cmp>, <id>0x0000005b</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpEL6751CanDrv</cmp>, <id>0x00005f0b</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpDynamicText</cmp>, <id>0x00000051</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpDevice</cmp>, <id>0x0000000e</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCryptMD5</cmp>, <id>0x0000006a</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCoreDump</cmp>, <id>0x00000083</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCommunicationLib</cmp>, <id>0x0000000c</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCodeMeter</cmp>, <id>0x0000007a</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpChecksum</cmp>, <id>0x0000000b</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCharDevice</cmp>, <id>0x00000300</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpChannelServer</cmp>, <id>0x0000000a</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpChannelMgr</cmp>, <id>0x00000009</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpChannelClientIec</cmp>, <id>0x0000005d</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpChannelClient</cmp>, <id>0x00000008</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAATypes</cmp>, <id>0x00004006</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAATimer</cmp>, <id>0x00004016</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAATickUtil</cmp>, <id>0x00004010</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAATick</cmp>, <id>0x00004009</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAAStorage</cmp>, <id>0x0000007e</id> <ver>3.5.11.10</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAASerialCom</cmp>, <id>0x00004012</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAASegBufferMan</cmp>, <id>0x00004019</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoServer</cmp>, <id>0x00004017</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoClient</cmp>, <id>0x00004011</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAARealTimeClock</cmp>, <id>0x00004014</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAANetBaseServices</cmp>, <id>0x00004018</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAAMemBlockMan</cmp>, <id>0x00004003</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAAFile</cmp>, <id>0x00004008</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAADTUtil</cmp>, <id>0x00004013</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAACanL2</cmp>, <id>0x00004004</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAACallback</cmp>, <id>0x00004001</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAABehaviourModel</cmp>, <id>0x00004015</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpCAAAsyncMan</cmp>, <id>0x00004007</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvUdp</cmp>, <id>0x00000007</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvTcp</cmp>, <id>0x00000030</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpBitmapPool</cmp>, <id>0x00000050</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtilIec</cmp>, <id>0x0000005c</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtil</cmp>, <id>0x00000004</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpBACnet</cmp>, <id>0x00000400</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpAsyncMgr</cmp>, <id>0x0000005f</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpAppForce</cmp>, <id>0x00000074</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpAppBP</cmp>, <id>0x00000073</id> <ver>3.5.11.0</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpApp</cmp>, <id>0x00000002</id> <ver>3.5.11.20</ver>
1514495832, 0x00000001, 1, 0, 10, <cmp>CmpAlarmManager</cmp>, <id>0x0000007c</id> <ver>3.5.11.10</ver>
1514495832, 0x00000104, 1, 0, 1, PlcLogicPrefix=0: Execute online command ResetOrginDevice to enable backup/restore feature
1514495832, 0x0000000a, 1, 0, 0, <numofchannels>4</numofchannels> channels available, each of the size <buffersize>100000</buffersize> Bytes
1514495832, 0x00000009, 1, 0, 2, Running as network server
1514495832, 0x00000009, 1, 0, 1, Running as network client
1514495832, 0x00000007, 1, 0, 6, Network interface: <ipaddress>192.168.1.33</ipaddress>, subnetmask <subnetmask>255.255.255.0</subnetmask>
1514495832, 0x00000018, 1, 0, 4, Network interface <interface>ether 1</interface> at router <instance>0</instance> registered
1514495832, 0x00005f0d, 1, 0, 1, interface <interface>can0</interface> is not available
1514495832, 0x00000124, 1, 0, 0, **********
1514495832, 0x00000124, 1, 0, 0, OPC UA Server Started:
1514495832, 0x00000124, 1, 0, 0, Hostname: raspberry, Port: 4840
1514495832, 0x00000124, 1, 0, 0, URL: opc.tcp://raspberry:4840
1514495832, 0x00000124, 1, 0, 0, Loopbackadapter activated.
1514495832, 0x00000124, 1, 0, 0, All available networkadapters are used.
1514495832, 0x00000124, 1, 0, 0, *********
1514495832, 0x00000124, 1, 0, 0, Provider CODESYS_DefaultProvider with Version 0x3050b0a registerd at the OPC UA server.
1514495832, 0x00000124, 1, 0, 0, Provider CmpOPCUAProviderIecVarAccess with Version 0x3050b14 registerd at the OPC UA server.
1514495832, 0x00000030, 1, 0, 6, Local network address: <ipaddress>192.168.1.33</ipaddress>
1514495832, 0x00000018, 1, 0, 4, Network interface <interface>BlkDrvTcp</interface> at router <instance>1</instance> registered
1514495832, 0x00000018, 1, 0, 1, Setting router <instance>0</instance> address to
1514495832, 0x00000018, 1, 0, 1, Setting router <instance>1</instance> address to (2ddc:c0a8:0121)
1514495837, 0x00000126, 1, 0, 0, Valid license found for OPC UA IecVarAccess provider.
1514495837, 0x00000002, 1, 0, 7, Retains matched to bootproject of application [<app>Application</app>]
1514495837, 0x00000002, 1, 0, 6, Bootproject of application [<app>Application</app>] loaded
1514495837, 0x00000002, 1, 0, 10, Application [<app>Application</app>] started
1514495837, 0x00000001, 1, 0, 34, CODESYS Control ready
1514495837, 0x0000100c, 1, 0, 0, Visuinitialization starting.
1514495837, 0x00001012, 4, 0, 0, Database Error in method DetermineRootPages: Error code = 30531, Action = 1030
1514495837, 0x00001012, 4, 0, 0, Database Error in method CyclicCall: Error code = 30531, Action = 1030
1514495837, 0x0000100c, 1, 0, 0, Visuinitialization done.
1514495837, 0x00000071, 1, 0, 0, ********
1514495837, 0x00000071, 1, 0, 0, Web Server
1514495837, 0x00000071, 1, 0, 0, Root directory : $PlcLogic$/$visu$
1514495837, 0x00000071, 1, 0, 0, Host : raspberry
1514495837, 0x00000071, 1, 0, 0, HTTP port : 8080
1514495837, 0x00000071, 1, 0, 0, HTTPS port : 443
1514495837, 0x00000071, 1, 0, 0, Connection type : HTTP
1514495837, 0x00000071, 1, 0, 0, ********
1514499012, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/webvisu.cfg.json</file> requested ...
1514499012, 0x00000071, 1, 0, 0, State: successful
1514499012, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/application.imagepoolcollection.csv</file> requested ...
1514499012, 0x00000071, 1, 0, 0, State: successful
1514499012, 0x00000072, 1, 0, 0, Localhost connection established ...
1514499013, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client for Extern-ID: 17096
1514499013, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client successful for Extern-ID: 17096 Returned IEC-ID: 0
1514499065, 0x00000001, 2, 0, 0, no runtime license - running in demo mode(~119 minutes)
1514500543, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/webvisu.cfg.json</file> requested ...
1514500543, 0x00000071, 1, 0, 0, State: successful
1514500543, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/application.imagepoolcollection.csv</file> requested ...
1514500543, 0x00000071, 1, 0, 0, State: successful
1514500543, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client for Extern-ID: 17098
1514500543, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client successful for Extern-ID: 17098 Returned IEC-ID: 1
1514502810, 0x0000100c, 1, 0, 0, VisuFctCheckForUnusedClients: Removing Client at Address: 1990300664
1514502810, 0x0000100c, 1, 0, 0, VisuFctCheckForUnusedClients: Successfully Removed Client at Address: 1990300664, IEC-ID was: 1
1514506478, 0x00000001, 1, 0, 35, CODESYS Control shutdown...
1514506478, 0x00000071, 1, 0, 13, Webserver stopped
1514506478, 0x0000100c, 1, 0, 0, Visu_PRG: Successfully Removed Client with IEC-ID: 0
1514506479, 0x00000071, 2, 0, 14, Unbalanced calls to WebServerRequestRunning/WebServerReleaseRunning
1514506479, 0x00000124, 1, 0, 0, Provider CODESYS_DefaultProvider with Version 0x3050b0a unregisterd at the OPC UA server.
1514506479, 0x00000124, 1, 0, 0, Provider CmpOPCUAProviderIecVarAccess with Version 0x3050b14 unregisterd at the OPC UA server.
1514506479, 0x00000018, 1, 0, 5, Network interface <interface>BlkDrvTcp</interface> unregistered
1514506479, 0x00000124, 1, 0, 0, *** Server OPC UA stopped! *****
1514506479, 0x00000018, 1, 0, 5, Network interface <interface>ether 1</interface> unregistered
Hi,
Here is the file when I restart it with the command:
sudo service codesyscontrol start
;*********
(0021);<loggername>/tmp/codesyscontrol.log</loggername>
;<logoptions>
; <enable>1</enable>
; <type>normal</type>
; <timestamp>rtc</timestamp>
; <deactivatable>0</deactivatable>
; <dump>always</dump>
; <filter>0x0000000f<filter>
; <maxentries>1000</maxentries>
; <maxfiles>1</maxfiles>
; <maxfilesize>1000000</maxfilesize>
;</filter></filter></logoptions>
;<entries>
;Timestamp, CmpId, ClassId, ErrorId, InfoId, InfoText
;</entries>
;*********
1514539265, 0x00000013, 1, 0, 0, <logoptions>
1514539265, 0x00000013, 1, 0, 0, <benable>1</benable>
1514539265, 0x00000013, 1, 0, 0, <type>normal</type>
1514539265, 0x00000013, 1, 0, 0, <timestamp>rtc</timestamp>
1514539265, 0x00000013, 1, 0, 0, <disableable>0</disableable>
1514539265, 0x00000013, 1, 0, 0, <filter>0x0000000f<filter>
1514539265, 0x00000013, 1, 0, 0, <maxentries>1000</maxentries>
1514539265, 0x00000013, 1, 0, 0, <maxfiles>1</maxfiles>
1514539265, 0x00000013, 1, 0, 0, <maxfilesize>1000000</maxfilesize>
1514539265, 0x00000013, 1, 0, 0, </filter></filter></logoptions>
1514539265, 0x00000001, 1, 0, 4, CODESYS Control V3
1514539265, 0x00000001, 1, 0, 5, Copyright (c) 3S - Smart Software Solutions GmbH
1514539265, 0x00000001, 1, 0, 6, <version>3.5.11.20</version> <builddate>Sep 15 2017</builddate>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>CM</cmp>, <id>0x00000001</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>CmpMemPool</cmp>, <id>0x0000001e</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>CmpLog</cmp>, <id>0x00000013</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>CmpSettings</cmp>, <id>0x0000001a</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysFile</cmp>, <id>0x00000104</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysTimer</cmp>, <id>0x00000116</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysTimeRtc</cmp>, <id>0x00000127</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysTime</cmp>, <id>0x00000115</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysTask</cmp>, <id>0x00000114</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysTarget</cmp>, <id>0x00000112</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysSocket</cmp>, <id>0x00000111</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysShm</cmp>, <id>0x00000110</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysSemProcess</cmp>, <id>0x00000119</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysSemCount</cmp>, <id>0x00000139</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysSem</cmp>, <id>0x0000010f</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysReadWriteLock</cmp>, <id>0x0000013e</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysProcess</cmp>, <id>0x0000010e</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysOut</cmp>, <id>0x0000010b</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysMutex</cmp>, <id>0x0000013a</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysMsgQ</cmp>, <id>0x0000010a</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysModule</cmp>, <id>0x00000109</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysMem</cmp>, <id>0x00000108</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysInternalLib</cmp>, <id>0x00000107</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>_</cmp>, <id>0x00000103</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysEvent</cmp>, <id>0x00000102</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysEthernet</cmp>, <id>0x0000011c</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysDir</cmp>, <id>0x0000011b</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysCpuHandling</cmp>, <id>0x00000101</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, System: <cmp>SysCom</cmp>, <id>0x00000100</id> <ver>3.5.11.10</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpWebServerHandlerV3</cmp>, <id>0x00000072</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpWebServer</cmp>, <id>0x00000071</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpVisuServer</cmp>, <id>0x00000057</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpVisuHandler</cmp>, <id>0x00000054</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpUserMgr</cmp>, <id>0x00000061</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpUserDB</cmp>, <id>0x00000064</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpTraceMgr</cmp>, <id>0x00000070</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpSrv</cmp>, <id>0x0000001c</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpSocketCanDrv</cmp>, <id>0x00005f0d</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpSchedule</cmp>, <id>0x00000019</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpRouter</cmp>, <id>0x00000018</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpRetain</cmp>, <id>0x00000017</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpRasPi</cmp>, <id>0x00000089</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpPlcShell</cmp>, <id>0x00000128</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpOpenSSL</cmp>, <id>0x00000033</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAStack</cmp>, <id>0x0000008d</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAServer</cmp>, <id>0x00000124</id> <ver>3.5.11.10</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAProviderIecVarAccess</cmp>, <id>0x00000126</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceServer</cmp>, <id>0x00000016</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClientIec</cmp>, <id>0x0000011d</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClient</cmp>, <id>0x00000015</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpMonitor2</cmp>, <id>0x00000032</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpIoMgr</cmp>, <id>0x00000012</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpIoDrvIec</cmp>, <id>0x0000005a</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpIecVarAccess</cmp>, <id>0x00000060</id> <ver>3.5.11.10</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpIecTask</cmp>, <id>0x00000011</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpIecStringUtils</cmp>, <id>0x0000007f</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpGwCommDrvTcp</cmp>, <id>0x00000010</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpGateway</cmp>, <id>0x0000000f</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpFileTransfer</cmp>, <id>0x0000005e</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpEventMgr</cmp>, <id>0x0000005b</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpEL6751CanDrv</cmp>, <id>0x00005f0b</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpDynamicText</cmp>, <id>0x00000051</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpDevice</cmp>, <id>0x0000000e</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCryptMD5</cmp>, <id>0x0000006a</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCoreDump</cmp>, <id>0x00000083</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCommunicationLib</cmp>, <id>0x0000000c</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCodeMeter</cmp>, <id>0x0000007a</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpChecksum</cmp>, <id>0x0000000b</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCharDevice</cmp>, <id>0x00000300</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpChannelServer</cmp>, <id>0x0000000a</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpChannelMgr</cmp>, <id>0x00000009</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpChannelClientIec</cmp>, <id>0x0000005d</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpChannelClient</cmp>, <id>0x00000008</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAATypes</cmp>, <id>0x00004006</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAATimer</cmp>, <id>0x00004016</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAATickUtil</cmp>, <id>0x00004010</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAATick</cmp>, <id>0x00004009</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAAStorage</cmp>, <id>0x0000007e</id> <ver>3.5.11.10</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAASerialCom</cmp>, <id>0x00004012</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAASegBufferMan</cmp>, <id>0x00004019</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoServer</cmp>, <id>0x00004017</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoClient</cmp>, <id>0x00004011</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAARealTimeClock</cmp>, <id>0x00004014</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAANetBaseServices</cmp>, <id>0x00004018</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAAMemBlockMan</cmp>, <id>0x00004003</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAAFile</cmp>, <id>0x00004008</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAADTUtil</cmp>, <id>0x00004013</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAACanL2</cmp>, <id>0x00004004</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAACallback</cmp>, <id>0x00004001</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAABehaviourModel</cmp>, <id>0x00004015</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpCAAAsyncMan</cmp>, <id>0x00004007</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvUdp</cmp>, <id>0x00000007</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvTcp</cmp>, <id>0x00000030</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpBitmapPool</cmp>, <id>0x00000050</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtilIec</cmp>, <id>0x0000005c</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtil</cmp>, <id>0x00000004</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpBACnet</cmp>, <id>0x00000400</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpAsyncMgr</cmp>, <id>0x0000005f</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpAppForce</cmp>, <id>0x00000074</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpAppBP</cmp>, <id>0x00000073</id> <ver>3.5.11.0</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpApp</cmp>, <id>0x00000002</id> <ver>3.5.11.20</ver>
1514539265, 0x00000001, 1, 0, 10, <cmp>CmpAlarmManager</cmp>, <id>0x0000007c</id> <ver>3.5.11.10</ver>
1514539265, 0x00000104, 1, 0, 1, PlcLogicPrefix=0: Execute online command ResetOrginDevice to enable backup/restore feature
1514539265, 0x0000000a, 1, 0, 0, <numofchannels>4</numofchannels> channels available, each of the size <buffersize>100000</buffersize> Bytes
1514539265, 0x00000009, 1, 0, 2, Running as network server
1514539265, 0x00000009, 1, 0, 1, Running as network client
1514539265, 0x00000007, 1, 0, 6, Network interface: <ipaddress>192.168.1.33</ipaddress>, subnetmask <subnetmask>255.255.255.0</subnetmask>
1514539265, 0x00000018, 1, 0, 4, Network interface <interface>ether 1</interface> at router <instance>0</instance> registered
1514539265, 0x00005f0d, 1, 0, 1, interface <interface>can0</interface> is not available
1514539265, 0x00000124, 1, 0, 0, **********
1514539265, 0x00000124, 1, 0, 0, OPC UA Server Started:
1514539265, 0x00000124, 1, 0, 0, Hostname: raspberry, Port: 4840
1514539265, 0x00000124, 1, 0, 0, URL: opc.tcp://raspberry:4840
1514539265, 0x00000124, 1, 0, 0, Loopbackadapter activated.
1514539265, 0x00000124, 1, 0, 0, All available networkadapters are used.
1514539265, 0x00000124, 1, 0, 0, *********
1514539265, 0x00000124, 1, 0, 0, Provider CODESYS_DefaultProvider with Version 0x3050b0a registerd at the OPC UA server.
1514539265, 0x00000124, 1, 0, 0, Provider CmpOPCUAProviderIecVarAccess with Version 0x3050b14 registerd at the OPC UA server.
1514539265, 0x00000030, 1, 0, 6, Local network address: <ipaddress>192.168.1.33</ipaddress>
1514539265, 0x00000018, 1, 0, 4, Network interface <interface>BlkDrvTcp</interface> at router <instance>1</instance> registered
1514539265, 0x00000018, 1, 0, 1, Setting router <instance>0</instance> address to
1514539265, 0x00000018, 1, 0, 1, Setting router <instance>1</instance> address to (2ddc:c0a8:0121)
1514539268, 0x00000126, 1, 0, 0, Valid license found for OPC UA IecVarAccess provider.
1514539268, 0x00000002, 1, 0, 7, Retains matched to bootproject of application [<app>Application</app>]
1514539268, 0x00000002, 1, 0, 6, Bootproject of application [<app>Application</app>] loaded
1514539268, 0x00000002, 1, 0, 10, Application [<app>Application</app>] started
1514539268, 0x00000001, 1, 0, 34, CODESYS Control ready
1514539268, 0x0000100c, 1, 0, 0, Visuinitialization starting.
1514539268, 0x00001012, 4, 0, 0, Database Error in method DetermineRootPages: Error code = 30531, Action = 1030
1514539268, 0x00001012, 4, 0, 0, Database Error in method CyclicCall: Error code = 30531, Action = 1030
1514539268, 0x0000100c, 1, 0, 0, Visuinitialization done.
1514539268, 0x00000071, 1, 0, 0, ********
1514539268, 0x00000071, 1, 0, 0, Web Server
1514539268, 0x00000071, 1, 0, 0, Root directory : $PlcLogic$/$visu$
1514539268, 0x00000071, 1, 0, 0, Host : raspberry
1514539268, 0x00000071, 1, 0, 0, HTTP port : 8080
1514539268, 0x00000071, 1, 0, 0, HTTPS port : 443
1514539268, 0x00000071, 1, 0, 0, Connection type : HTTP
1514539268, 0x00000071, 1, 0, 0, ***********
1514539272, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/webvisu.cfg.json</file> requested ...
1514539272, 0x00000071, 1, 0, 0, State: successful
1514539272, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/application.imagepoolcollection.csv</file> requested ...
1514539272, 0x00000071, 1, 0, 0, State: successful
1514539272, 0x00000072, 1, 0, 0, Localhost connection established ...
1514539273, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client for Extern-ID: 284469
1514539273, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client successful for Extern-ID: 284469 Returned IEC-ID: 0
1514539273, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/webvisu.cfg.json</file> requested ...
1514539273, 0x00000071, 1, 0, 0, State: successful
1514539274, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/application.imagepoolcollection.csv</file> requested ...
1514539274, 0x00000071, 1, 0, 0, State: successful
1514539280, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client for Extern-ID: 284471
1514539280, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client successful for Extern-ID: 284471 Returned IEC-ID: 1
Hi,
Browsing the files, I observe that the raspberry pi starts in demo mode .Hors I turn with a license for 2 years ...
I do not understand...
Hi,
you could relicense with the CMLicenseNew.WibuCmRaU file..
see the FAQ's.
User the CODESYS file browser to save the CMLicenseNew.WibuCmRaU to your pc
and then reativate it.
(Before you do this... clean up the content cmact_license Directory - means delete the content) and restart the PI plc...
Then reactivate by this file.
BR
Edwin
Hi,
Β if I do SSH:
sudo reboot, here is the contents of the file.It does not indicate more mode DEMO
pi@raspberry ~ $ cat /tmp/codesyscontrol.log
(0021);*********
;<loggername>/tmp/codesyscontrol.log</loggername>
;<logoptions>
; <enable>1</enable>
; <type>normal</type>
; <timestamp>rtc</timestamp>
; <deactivatable>0</deactivatable>
; <dump>always</dump>
; <filter>0x0000000f<filter>
; <maxentries>1000</maxentries>
; <maxfiles>1</maxfiles>
; <maxfilesize>1000000</maxfilesize>
;</filter></filter></logoptions>
;<entries>
;Timestamp, CmpId, ClassId, ErrorId, InfoId, InfoText
;</entries>
;*********
1514548307, 0x00000013, 1, 0, 0, <logoptions>
1514548307, 0x00000013, 1, 0, 0, <benable>1</benable>
1514548307, 0x00000013, 1, 0, 0, <type>normal</type>
1514548307, 0x00000013, 1, 0, 0, <timestamp>rtc</timestamp>
1514548307, 0x00000013, 1, 0, 0, <disableable>0</disableable>
1514548307, 0x00000013, 1, 0, 0, <filter>0x0000000f<filter>
1514548307, 0x00000013, 1, 0, 0, <maxentries>1000</maxentries>
1514548307, 0x00000013, 1, 0, 0, <maxfiles>1</maxfiles>
1514548307, 0x00000013, 1, 0, 0, <maxfilesize>1000000</maxfilesize>
1514548307, 0x00000013, 1, 0, 0, </filter></filter></logoptions>
1514548307, 0x00000001, 1, 0, 4, CODESYS Control V3
1514548307, 0x00000001, 1, 0, 5, Copyright (c) 3S - Smart Software Solutions GmbH
1514548307, 0x00000001, 1, 0, 6, <version>3.5.11.20</version> <builddate>Sep 15 2017</builddate>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>CM</cmp>, <id>0x00000001</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>CmpMemPool</cmp>, <id>0x0000001e</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>CmpLog</cmp>, <id>0x00000013</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>CmpSettings</cmp>, <id>0x0000001a</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysFile</cmp>, <id>0x00000104</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysTimer</cmp>, <id>0x00000116</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysTimeRtc</cmp>, <id>0x00000127</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysTime</cmp>, <id>0x00000115</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysTask</cmp>, <id>0x00000114</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysTarget</cmp>, <id>0x00000112</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysSocket</cmp>, <id>0x00000111</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysShm</cmp>, <id>0x00000110</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysSemProcess</cmp>, <id>0x00000119</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysSemCount</cmp>, <id>0x00000139</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysSem</cmp>, <id>0x0000010f</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysReadWriteLock</cmp>, <id>0x0000013e</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysProcess</cmp>, <id>0x0000010e</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysOut</cmp>, <id>0x0000010b</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysMutex</cmp>, <id>0x0000013a</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysMsgQ</cmp>, <id>0x0000010a</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysModule</cmp>, <id>0x00000109</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysMem</cmp>, <id>0x00000108</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysInternalLib</cmp>, <id>0x00000107</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>_</cmp>, <id>0x00000103</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysEvent</cmp>, <id>0x00000102</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysEthernet</cmp>, <id>0x0000011c</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysDir</cmp>, <id>0x0000011b</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysCpuHandling</cmp>, <id>0x00000101</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, System: <cmp>SysCom</cmp>, <id>0x00000100</id> <ver>3.5.11.10</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpWebServerHandlerV3</cmp>, <id>0x00000072</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpWebServer</cmp>, <id>0x00000071</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpVisuServer</cmp>, <id>0x00000057</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpVisuHandler</cmp>, <id>0x00000054</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpUserMgr</cmp>, <id>0x00000061</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpUserDB</cmp>, <id>0x00000064</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpTraceMgr</cmp>, <id>0x00000070</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpSrv</cmp>, <id>0x0000001c</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpSocketCanDrv</cmp>, <id>0x00005f0d</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpSchedule</cmp>, <id>0x00000019</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpRouter</cmp>, <id>0x00000018</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpRetain</cmp>, <id>0x00000017</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpRasPi</cmp>, <id>0x00000089</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpPlcShell</cmp>, <id>0x00000128</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpOpenSSL</cmp>, <id>0x00000033</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAStack</cmp>, <id>0x0000008d</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAServer</cmp>, <id>0x00000124</id> <ver>3.5.11.10</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpOPCUAProviderIecVarAccess</cmp>, <id>0x00000126</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceServer</cmp>, <id>0x00000016</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClientIec</cmp>, <id>0x0000011d</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpNameServiceClient</cmp>, <id>0x00000015</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpMonitor2</cmp>, <id>0x00000032</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpIoMgr</cmp>, <id>0x00000012</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpIoDrvIec</cmp>, <id>0x0000005a</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpIecVarAccess</cmp>, <id>0x00000060</id> <ver>3.5.11.10</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpIecTask</cmp>, <id>0x00000011</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpIecStringUtils</cmp>, <id>0x0000007f</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpGwCommDrvTcp</cmp>, <id>0x00000010</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpGateway</cmp>, <id>0x0000000f</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpFileTransfer</cmp>, <id>0x0000005e</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpEventMgr</cmp>, <id>0x0000005b</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpEL6751CanDrv</cmp>, <id>0x00005f0b</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpDynamicText</cmp>, <id>0x00000051</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpDevice</cmp>, <id>0x0000000e</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCryptMD5</cmp>, <id>0x0000006a</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCoreDump</cmp>, <id>0x00000083</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCommunicationLib</cmp>, <id>0x0000000c</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCodeMeter</cmp>, <id>0x0000007a</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpChecksum</cmp>, <id>0x0000000b</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCharDevice</cmp>, <id>0x00000300</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpChannelServer</cmp>, <id>0x0000000a</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpChannelMgr</cmp>, <id>0x00000009</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpChannelClientIec</cmp>, <id>0x0000005d</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpChannelClient</cmp>, <id>0x00000008</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAATypes</cmp>, <id>0x00004006</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAATimer</cmp>, <id>0x00004016</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAATickUtil</cmp>, <id>0x00004010</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAATick</cmp>, <id>0x00004009</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAAStorage</cmp>, <id>0x0000007e</id> <ver>3.5.11.10</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAASerialCom</cmp>, <id>0x00004012</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAASegBufferMan</cmp>, <id>0x00004019</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoServer</cmp>, <id>0x00004017</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAASdoClient</cmp>, <id>0x00004011</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAARealTimeClock</cmp>, <id>0x00004014</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAANetBaseServices</cmp>, <id>0x00004018</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAAMemBlockMan</cmp>, <id>0x00004003</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAAFile</cmp>, <id>0x00004008</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAADTUtil</cmp>, <id>0x00004013</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAACanL2</cmp>, <id>0x00004004</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAACallback</cmp>, <id>0x00004001</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAABehaviourModel</cmp>, <id>0x00004015</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpCAAAsyncMan</cmp>, <id>0x00004007</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvUdp</cmp>, <id>0x00000007</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpBlkDrvTcp</cmp>, <id>0x00000030</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpBitmapPool</cmp>, <id>0x00000050</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtilIec</cmp>, <id>0x0000005c</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpBinTagUtil</cmp>, <id>0x00000004</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpBACnet</cmp>, <id>0x00000400</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpAsyncMgr</cmp>, <id>0x0000005f</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpAppForce</cmp>, <id>0x00000074</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpAppBP</cmp>, <id>0x00000073</id> <ver>3.5.11.0</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpApp</cmp>, <id>0x00000002</id> <ver>3.5.11.20</ver>
1514548307, 0x00000001, 1, 0, 10, <cmp>CmpAlarmManager</cmp>, <id>0x0000007c</id> <ver>3.5.11.10</ver>
1514548307, 0x00000104, 1, 0, 1, PlcLogicPrefix=0: Execute online command ResetOrginDevice to enable backup/restore feature
1514548307, 0x0000000a, 1, 0, 0, <numofchannels>4</numofchannels> channels available, each of the size <buffersize>100000</buffersize> Bytes
1514548307, 0x00000009, 1, 0, 2, Running as network server
1514548307, 0x00000009, 1, 0, 1, Running as network client
1514548307, 0x00000007, 1, 0, 6, Network interface: <ipaddress>192.168.1.33</ipaddress>, subnetmask <subnetmask>255.255.255.0</subnetmask>
1514548307, 0x00000018, 1, 0, 4, Network interface <interface>ether 1</interface> at router <instance>0</instance> registered
1514548307, 0x00005f0d, 1, 0, 1, interface <interface>can0</interface> is not available
1514548307, 0x00000124, 1, 0, 0, **********
1514548307, 0x00000124, 1, 0, 0, OPC UA Server Started:
1514548307, 0x00000124, 1, 0, 0, Hostname: raspberry, Port: 4840
1514548307, 0x00000124, 1, 0, 0, URL: opc.tcp://raspberry:4840
1514548307, 0x00000124, 1, 0, 0, Loopbackadapter activated.
1514548307, 0x00000124, 1, 0, 0, All available networkadapters are used.
1514548307, 0x00000124, 1, 0, 0, *********
1514548307, 0x00000124, 1, 0, 0, Provider CODESYS_DefaultProvider with Version 0x3050b0a registerd at the OPC UA server.
1514548307, 0x00000124, 1, 0, 0, Provider CmpOPCUAProviderIecVarAccess with Version 0x3050b14 registerd at the OPC UA server.
1514548307, 0x00000030, 1, 0, 6, Local network address: <ipaddress>192.168.1.33</ipaddress>
1514548307, 0x00000018, 1, 0, 4, Network interface <interface>BlkDrvTcp</interface> at router <instance>1</instance> registered
1514548307, 0x00000018, 1, 0, 1, Setting router <instance>0</instance> address to
1514548307, 0x00000018, 1, 0, 1, Setting router <instance>1</instance> address to (2ddc:c0a8:0121)
1514548311, 0x00000126, 1, 0, 0, Valid license found for OPC UA IecVarAccess provider.
1514548311, 0x00000002, 1, 0, 7, Retains matched to bootproject of application [<app>Application</app>]
1514548311, 0x00000002, 1, 0, 6, Bootproject of application [<app>Application</app>] loaded
1514548311, 0x00000002, 1, 0, 10, Application [<app>Application</app>] started
1514548311, 0x00000001, 1, 0, 34, CODESYS Control ready
1514548311, 0x0000100c, 1, 0, 0, Visuinitialization starting.
1514548311, 0x00001012, 4, 0, 0, Database Error in method DetermineRootPages: Error code = 30531, Action = 1030
1514548311, 0x00001012, 4, 0, 0, Database Error in method CyclicCall: Error code = 30531, Action = 1030
1514548312, 0x0000100c, 1, 0, 0, Visuinitialization done.
1514548312, 0x00000071, 1, 0, 0, ********
1514548312, 0x00000071, 1, 0, 0, Web Server
1514548312, 0x00000071, 1, 0, 0, Root directory : $PlcLogic$/$visu$
1514548312, 0x00000071, 1, 0, 0, Host : raspberry
1514548312, 0x00000071, 1, 0, 0, HTTP port : 8080
1514548312, 0x00000071, 1, 0, 0, HTTPS port : 443
1514548312, 0x00000071, 1, 0, 0, Connection type : HTTP
1514548312, 0x00000071, 1, 0, 0, ***********
1514548332, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/webvisu.cfg.json</file> requested ...
1514548332, 0x00000071, 1, 0, 0, State: successful
1514548332, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/application.imagepoolcollection.csv</file> requested ...
1514548332, 0x00000071, 1, 0, 0, State: successful
1514548333, 0x00000072, 1, 0, 0, Localhost connection established ...
1514548333, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client for Extern-ID: 15440
1514548333, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client successful for Extern-ID: 15440 Returned IEC-ID: 0
1514548336, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/webvisu.cfg.json</file> requested ...
1514548336, 0x00000071, 1, 0, 0, State: successful
1514548337, 0x00000071, 1, 0, 0, File <file>$PlcLogic$/$visu$/application.imagepoolcollection.csv</file> requested ...
1514548337, 0x00000071, 1, 0, 0, State: successful
1514548343, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client for Extern-ID: 15442
1514548343, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client successful for Extern-ID: 15442 Returned IEC-ID: 1
l viewtopic.php?f=22&t=5641&p=10690#p10690 l
Hi ,
My file is 116.1 kb and I see that it must be between 130 and 140 kb.
Confirm that my file is empty?
I do not have a backup. Is there a way to recover the license otherwise?
Hi,
Looks okay,
use the CMLicenseNew.WibuCmRaU to reactivate the license, this will work.
BR
Edwin
Hi,
I did the manipulation as described above, and it works again ...
Thank you for your help
Hi,
this 'manipulation' is the recommended 'retore the license' procedure,
I would recommend to prefer to use it in compare to the using of the 'tar' file method.
BR
Edwin
Hi there,
I am not sure if I had the exact same problem, but my visualisation also stopped working after 8 hours or so, giving
me the VisuFctCheckForUnusedClients error (Removing Client at address xxx), and Channel closed because unused for 60s.
This Raspberry had already been Licensed!
What seemed to be the problem, whas that the operating mode in codesys was still switched to debug mode.
In the taskbar at the top of Codesys, go to: Online --> Operating Mode --> Select "Operational"
Not 100% sure that this is the reason why I got the same error message, and my Visu Crashing after 8 hours, but it seems to
be running fine now for the last 12 hours..
you need to add logfiles ...
cat /tmp/codesyscontrol.log
then we could check.
If it is really urgend sure it is aleways possible to use a support ticket.
BR
Edwin