I use softmotion with Beckhoff ethercat, EK1100 and EL7031 drive for the motor.
Everything works ok, but if I logout and login again I always get an error on the EL7031: bus not running.
Ethercat and EK1100 are OK
Same issue on normal PC and on raspberry Pi
I think this is safety issue to prevent unwanted motion after a stop.
can only solve this to download the program again.
How can I solve this or I,m I doing something wrong?
Error appears when I stop the plc running and start again
if I logout with plc running and log in again it is ok.
plc log :
AL status read from slave adress1002 status 16#18
watchdog for opmode expired.adress1002
(1002 =el7031)
ps: what should be setting of bus cycle task . use parent bus cycle settings or activate 1 or acivate 2
I have been playing with these setting , but what is the right setting .
for example I have an el1008 not working if I choose use parent bus cycle setting.
I find short description in:
ethercat mapping : tab <device>I/o mapping refresch variables , but it is not very clear to me .</device>
should work even with disconnected CODESYS..
Could you attache some plc log files?
Edwin,
plc log :
(1002 =el7031)
ok now it is clear please set the option update io's while plc in stop.
thx ,
works and solves other issues too