PostPosted: Wed Nov 29, 2017 8:27 am 
Offline

Joined: Fri Apr 14, 2017 9:39 pm
Posts: 3
In a project that uses CoDeSys 3.5 SP11, with Lexium 32M drives via EtherCAT, I had trouble ending the homing procedure. As can be seen from the chart, when the homing signal (blue track) returns to zero before the procedure is completed, the axis is stopped by the "MC_Halt" FB, which activates the "halt" bit of the word axis command, (green track). However, it can be seen from the red trace, when the axis velocity approaches zero (standstill?), The halt function concludes in advance of the stop motion and the axis resumes speed and continues the procedure of homing.
To prevent this from happening, for the moment I have extended the persistence to 1 of bit 8 on the axis command word.
The question is: Is there a way to adjust the SoftMotion library differently and do that, for example, do the functions consider the engine to be stopped with a bit delay or other adjustable, such as the zero speed threshold?


You do not have the required permissions to view the files attached to this post.


Top
   
PostPosted: Wed Nov 29, 2017 11:29 am 
Offline

Joined: Thu Jan 05, 2006 11:46 am
Posts: 34
Hello,

which homing routine do you are using? The homing driven by the drive executed with MC_Home or the SMC_homing from the PLC?

Bruno


Top
   
PostPosted: Thu Nov 30, 2017 8:18 am 
Offline

Joined: Fri Apr 14, 2017 9:39 pm
Posts: 3
Routine 26, driven by the drive and executed with MC_Home.


Top
   
PostPosted: Mon Dec 04, 2017 2:45 pm 
Offline

Joined: Thu Jan 05, 2006 11:46 am
Posts: 34
Hello,
normally the MC_Home is reporting a Done when the homing is finished.
Please keep the Execute on TRUE until you get the Done or an Error.

Bruno


Top
   
PostPosted: Sat Dec 09, 2017 11:13 pm 
Offline

Joined: Fri Apr 14, 2017 9:39 pm
Posts: 3
In my point of view, this is not the way for answer. That mean that the homing can't be halted? :shock:


Top
   
PostPosted: Tue Dec 12, 2017 9:16 am 
Offline

Joined: Thu Jan 05, 2006 11:46 am
Posts: 34
Hello,

a MC_Home could only be interrupted by a MC_Stop according PLCopen-state.
There is no HALT allowed and implemented in the driver to the softmotion-interface.

Bruno


Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 6 posts ] 

All times are UTC+01:00


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Limited