Codesys Control RTE

pedrazzi
2018-02-02
2018-02-02
  • pedrazzi - 2018-02-02

    Hi,
    i'm trying to run Codesys RTE on an industrial PC with Win7. The installation is ok and I can also Start the PLC.
    I make a new project on my laptop with the Codesys Control RTE Devive but I'm not able to can connect with the devive.
    I can ping the industrial PC but the Codesys network scan didn't see any device.

    Where is my fault, what i miss to do?
    thanks
    Simone

     
  • eschwellinger

    eschwellinger - 2018-02-02

    Hi,
    - check if you use Control RTE 64Bit - if yes you need to add the 64Bit device in the CODESYS project an vice versa..
    - check if the RTE is properly startet by - go with the mouse on the Task tray Icon - you should see the Network address which have been assigned.
    - remove the filter in the CODESYS scan Dialog/Settings to see all found devices on your network.
    BR
    Edwin

     