Author:  kumareasu [ Wed Jul 05, 2017 1:48 am ]
Post subject:  BBB Application Development

Hi,

Presently working with BeagleBoneBlack, trying with BBB with EK1100+EL2809+EL6080.
Could you please clarify the following....
1. My application is not getting started when power on the BBB.(Still I have not Activated lenience)
2. I am not able to map EL6080 for retentive variables.
3. Do we need to have proper shutdown of BBB or we can plug out the power(5V). Any feedback Data Corruption.
Regards,
Kumar Eswaran

Author:  Edwin Schwellinger [ Wed Aug 09, 2017 7:31 pm ]
Post subject:  Re: BBB Application Development

Hi,
1. My application is not getting started when power on the BBB.(Still I have not Activated lenience)
this should start, check the plclogger or do a cat /tmp/codesyscontrol.log to see details for the starting Problem

2. I am not able to map EL6080 for retentive variables.

see attached example but no further support from my side ;-(

3. Do we need to have proper shutdown of BBB or we can plug out the power(5V). Any feedback Data Corruption.

If not set to readonly in generell yes!

BR
Edwin