WAGO 750-8212 SUPPORT PROFINET (MASTER/SLAVE) ?

rajshaswat
2019-05-18
2019-05-20
  • rajshaswat - 2019-05-18

    Does anyone have configured WAGO 750-8212 Ethernet port for PROFINET (MASTER/SLAVE) using PFC200 SL runtime version.
    when i checked WAGO manual for 750-8212 communication protocol it does not specify for PROFINET communication support.
    but in PFC200 SL it is given for PROFINET support

    do any one have steps or idea for the configuration of PROFINET in 750-8212, does it has any limitation?
    as i have different device with different protocol.
    Ethernet i/p
    OPC UA
    Profinet

    IMG: FieldbusSupport.PNG

     
  • eschwellinger

    eschwellinger - 2019-05-18

    Hi,
    then performance of the PFC limits the pn devices you could add if you configure as profinet controller.
    Using profinet device sould work without prolems.

    fot the pn device you need to add in /etc/CODESYSControl_USer.cfg

    [SysSocket]
    Adapter.0.Name=br1
    Adapter.0.EnableSetIpAndMask=1

    See the example application here in this forum..

    BR
    Edwin

     
  • rajshaswat - 2019-05-20

    @Edwin Schwellinger So you suggest not to use Controller as Profinet device.
    Instead use Profinet device?

    I want to use this just for Communication between PLC-PLC or PLC to DCS over Profinet protocol.
    will i have some problem or limitation.

    I am not going to add any further Profinet device nor going to use any I/O device on Profinet protocol

     
  • eschwellinger

    eschwellinger - 2019-05-20

    Hi,

    then both either profinet controller or profinet device is possible sure..!

    BR
    Edwin

     