Hello, i have a strange behavior with an janz tec emPC imx6 and i use the last codesys control 3.5.11.20 for it ,
i want some data exchange with an Schneider M251.
The behavior is :
read 1 holding reg - OK,
read n holding reg not working, all values are set zero...,
with an modbus tcp scaner modscan32 i can read well from M251,
In M251 i use builtin modbus server..
any suggestions??? please...
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
Could you attach the project or at least screenshots?
Are you using the io varisbles in the pou's otherwise they will not be will updated.
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello, i have a strange behavior with an janz tec emPC imx6 and i use the last codesys control 3.5.11.20 for it ,
i want some data exchange with an Schneider M251.
The behavior is :
read 1 holding reg - OK,
read n holding reg not working, all values are set zero...,
with an modbus tcp scaner modscan32 i can read well from M251,
In M251 i use builtin modbus server..
any suggestions??? please...
tried also on raspberry the same behavior (
Hi,
Could you attach the project or at least screenshots?
Are you using the io varisbles in the pou's otherwise they will not be will updated.
BR
Edwin
thank you Edwin now works.