CODESYS V3+ WAGO PFC200+ MODBUS RTU

ZKh
2016-06-07
2017-03-30
  • ZKh - 2016-06-07

    Hi everyone
    I am new to CODESYS and Wago PFC200. I downloaded CODESYS 3.5.8 and PFC200 package manager. I also updated PFC200 package manager.
    I need to send and receive data between PFC200 and my slave device through Modbus RTU (RS485).
    I added all Modbus Libraries and PFC200 Libraries to my project.
    I inserted Modbus_com, Modbus_Master_COM_Port and Modbus_Slave_COM_Port into Devices tree.
    But when I login and start CPU, Modbus_Slave_COM_Port does not running.
    I also checked COM_Port, and there was no error!!
    I attached a screenshot of my project.

    Is there any possible solution?!!
    Thanks in advance

    IMG: ModbusRTU.png

     
  • eschwellinger

    eschwellinger - 2016-06-07

    Hi,
    did you change serial mode to rs485 in the plc shell?

    BR
    Edwin

    IMG: plcshell.jpg

     
  • ZKh - 2016-06-08

    Hi
    Dear Edwin

    Thanks a lot for your help. I change serial mode to RS485 in PLCshell succesfully.
    Now Modbus_Slave_COM_Port is running. But I have new problems to solve.
    first:
    I added Modbus_Slave_COM_Port to watch1. Before Modbus_Slave_COM_Port goes to running mode and response success; byModbusError changed between two values: Response_Timeout, Response_Wrong_Slave and m_DeviceState Changed Between: Unknown, Error for about a minute.
    I tried to solve this by changing response time but I sow no difference.
    Second:
    I want to read some values(Start Add:40001, Register Size:2, Type: Float) through RS485. I Think, I have some mistakes adding them to Modbus Slave Channel. the shown values are always 0 and I don't know how to map specific variables.

    I will attach screenshots.
    Thanks in advance

    IMG: Response.png

    IMG: ReadValues.png

     
  • eschwellinger

    eschwellinger - 2016-06-08

    Hi,

    you have two posibilities.
    1. Map variables .. give the Name there and use them in PLC_PRG Pou
    2. set alway update (this you could use for testing purpose)

    BR
    Edwin

    PS: Moderator should move the Topic to the CODESYS Control Posts!

    IMG: always.jpg

    IMG: Mapping.jpg

     
  • ZKh - 2016-06-11

    Hi

    Thanks a lot for your time and consideration.
    My slave has not running status again and I don't know why this happened!!!
    I moved the topic to CODESYS Control Posts.

    Thanks again

     
  • ZKh - 2016-07-03

    Hi
    Good news
    Finally I established a Modbus RTU (RS485) connection and I can read data from slave.
    I need data to update online but the problem is that, slave's data updates slowly
    I defined timeout responses as 1 second. Still not enough.
    Unfortunately adding data length makes updating slower.

    Is there any way to boost the update operation?

    Thanks in advance

     
  • johnlee - 2017-03-30

    I have done few project with Wago PLC from ECO to PFC, unlikely to tell you that Wago built in Com port always perform in low speed. If you need a good RS485 comport on wago plC, you have to use the wago high-end special com module, or direct go for TCP/IP to com port.

     