It is currently Fri Jul 19, 2019 6:46 am
Post new topic  This topic is locked, you cannot edit posts or make further replies.  [ 9 posts ]
 Post subject: Runtime
PostPosted: Fri Feb 28, 2014 9:19 am
CODESYS V3 Runtime
Control RTE stops under Windows 7 / Windows 8 after running 2 weeks
Control RTE Realtime capabilities: How to check if the bios settings are in the right condition for minimal jitter
Control RTE how to shutdown RTE triggered by VISU or IEC code
Persistence / Retain data : what is needed on plc side
Persistence/Retain data : when should you use NVRAM when UPS - what are is the advantage, disadvantage
How to use Control RTE on Notebooks with Ethercat -for testing purpose
Does Control RTE run on 64Bit Windows ?
Control RTE and Cifx Cards - how to setup the driver in windows hardware manager
PostPosted: Fri Feb 28, 2014 9:20 am
Problem: RTE stops after a certain time
Solution: Open Task Scheduler and disable the Power Efficiency Diagnostic
Disable by cmdline:
schtasks /change /TN "\Microsoft\Windows\Power Efficiency Diagnostics\AnalyzeSystem" /DISABLE
Back to FAQ overview
PostPosted: Fri Mar 07, 2014 7:20 am
How could we check if the realtime capabilities are ok with the bios Setting on my Windows platform?
1. After setting the bios according to the CoDeSysControlRTEV3_Manual.pdf (throtteling / speedstep / C-states must be switched off)
you need to check if your processor clock is stable.
A good tool to verify it / measure it is CPUZ (Google it).
Attention you should only execute either CPUZ or Control RTE not both at the same time (RTE will stop if you do it!)
2. Then Login to Control RTE with the project - check the taskmonitor - reset the jitter values (rightclick) then you should see values on the last row yellow marked
like in the attached screenshot
Generate high log on the RTE pc by opening IE / other applications and check if this has influence on the jitter values
PostPosted: Fri Mar 07, 2014 8:08 am
Question: Is it possible to shutdown the pc on which the RTE is running on, triggerd by the codesys application
Answer:
yes, there are two possibilities:
1. triggered by targetvisu:
% execute Command c:\WINDOWS\system32\shutdown.exe -s -t 00 -f', … siehe Screenshot
2. by iec code use SysProcessCreate (you need to add sysprocess.library)
SysProcessCreate(pszApplication:= 'c:\windows\system32\shutdown.exe', pszCommandLine:= '/p /f ', ulHide:= 0, pResult:= udiTemp);
PostPosted: Fri Mar 07, 2014 8:13 am
Question: What is needed to support persistent / retain data
Answer:
In general the plc should have a build in nvram or should be connected to an UPS (uninterrupted power supply)
PostPosted: Fri Mar 07, 2014 9:15 am
Question: What is the advanatge / disadvantage on using NVRAM - UPS(uninterruptable power supply )
The technical difference is:
NVRAM is a mapped area in which on each cycle the retain variable are updated
In case of using a UPS - this is the ram area and on shutdown of the runtime the runtime write the retain files (restore them on startup)
The result on this:
With nvram you have only a limited amount of retains for example 128k if the retain memory has this size.
With UPS there is not limit in size (sure your ram but this is nowadays not really a limit)
nvram: The cpu load (cycle time grow) could grow with increasing nvram occupancy, since this will lead to cyclic read and write access to this memory, for each used variable one access.
(Hint if you are using many retain variable with nvram:
Declare a structure which mirrors the retains data and copy the whole struct in the cycle, this is then only one access as oposed to many memory access if you have a bunch of single retain variables - this you should see immediately in the cycle time load)
PostPosted: Wed Jul 30, 2014 5:24 am
Is it possible to use my Notebook to have Control RTE and Ethercat running on it (Testing purpose)?
Yes this is possible if you use a Realtek RTL8111B / RTL8111D compatible ExpressCard
For Example: Exys 1GB Ethernet LAN ExpressCard EX-6087.
Take care on the bios settings / disable speedstep, c-states etc like in the RTE documentation is mentioned, to have a stable processor clock
in case you need hard realtime capabilities.
PostPosted: Wed Jul 30, 2014 5:29 am
Yes since 3.5SP5 Release there is a Setup available for 64Bit Control RTE.
Capable for Ethercat / SoftMotion / Visualization
/Profinet / Modbus / Ethernet IP / CANopen
PostPosted: Mon Oct 13, 2014 7:37 am
1. Control RTE and Cifx card, which driver do we need to install in windows device manager?
"c:\Program Files\3S CoDeSys\CODESYS Control RTE3\SysDrv3S\SysDrv3S.inf"
-see screenshot
2. Which settings are needed in CODESYSContol.cfg
depending which fieldbus system you want to use the, you need to select the right firmware image -
ProfibusMaster - cifxdpm.nxf
ProfinetMaster - cifxpnm.nxf
[CmpHilscherCIFX]
TraceLevel=0xFFFFFFFF
InterruptMode=0
DMAMode=1
Device.0.BootloaderFilePath=.\HilscherCIFX\Firmware\NETX100-BSL.bin
Device.0.Channel.0.FirmwareFile=.\HilscherCIFX\Firmware\cifxdpm.nxf
;Device.1.BootloaderFilePath=.\HilscherCIFX\Firmware\NETX100-BSL.bin
;Device.1.Channel.0.FirmwareFile=.\HilscherCIFX\Firmware\cifxpnm.nxf