ch341-uart usb/485 ->Program loaded Exception 3.5.8.0
hki75
2016-01-07
2016-01-08
  • hki75 - 2016-01-07
    I'm trying to start a MOdbus RTU comm between RPI2 and PC using usb/485 converter on RPI side.
    The converter is properly recognized by Raspbian : using the
    I get:
    I sent some char from RPI to PC by
    and it works
    and I add the following lines
    into /etc/CODESYSConfig.cfg
    but the runtime stay forced to stop cause of this:
    That seems to be correct..
    version i 3.5.8.0
    Some suggestion?
    IMG: Bild
    IMG: 2016
    eschwellinger - 2016-01-07
    check the plc logger.. for more details.
    the log seems do not show strange stuff..
    IMG: 2016
    hi,
    could not see any problem in the plc log...
    Could you give me a
    cat /tmp/codesyscontrol.log
    output here
    Linux version 4.1.13-v7+ (dc4@dc4-XPS13-9333) (gcc version 4.8.3 20140303 (prere lease) (crosstool-NG linaro-1.13.1+bzr2650 - Linaro GCC 2014.03) ) #826 SMP PREE MPT Fri Nov 13 20:19:03 GMT 2015
    PlcStartRasPI[760]: fork child: ppid: 408
    * CoDeSysControl DEMO VERSION - runs 2 hours*
    machine: armv7l
    timer resolution: 1nsec
    SysFileGetSize_[254]: stat(.UserMgmtDB.csv):No such file or directory
    SysFileGetSize_[254]: stat(UserMgmtDB.csv):No such file or directory
    SysFileGetSize_[254]: stat(.UserMgmtRightsDB.csv):No such file or directory
    SysFileGetSize_[254]: stat(UserMgmtRightsDB.csv):No such file or directory
    SysEthernetOSHookFunction[100]: changed protocol filter to 0x3
    [394]: setting fpu-exceptions failed
    Socket_CanMiniDriver_Setup[1007]: registering can interface 0
    openRxSocket[576]: Opened socket for reading (can0)
    openRxSocket[582]: ioctl(SIOCGIFINDEX): No such device
    SysTaskCreate[296]: create SchedProcessorLoad(prio:64,interval:0us,stacksize:131 072)
    SysTaskCreate[296]: create SchedException(prio:31,interval:0us,stacksize:131072)
    SysTaskFrame[230]: SchedProcessorLoad(tid:480,OSprio:0) running
    SysTaskFrame[230]: SchedException(tid:481,OSprio:68) running
    SysTaskCreate[296]: create Schedule(prio:5,interval:1000us,stacksize:131072)
    SysTaskFrame[230]: Schedule(tid:482,OSprio:94) running
    SysTaskCreate[296]: create CAAEventTask(prio:30,interval:0us,stacksize:131072)
    SysTaskFrame[230]: CAAEventTask(tid:483,OSprio:69) running
    SysFileDelete
    [192]: unlink(Application.xml):No such file or directory
    SysTaskCreate[296]: create IoMgrDiagTask(prio:192,interval:0us,stacksize:131072)
    SysTaskCreate[296]: create MainTask(prio:33,interval:20000us,stacksize:131072)
    SysTaskFrame[230]: IoMgrDiagTask(tid:484,OSprio:0) running
    SysTaskFrame[230]: MainTask(tid:485,OSprio:66) running
    SysFileGetSize_[254]: stat(Application.boot.xml):No such file or directory
    SysTaskCreate[296]: create BlkDrvTcp(prio:95,interval:0us,stacksize:131072)
    SysTaskCreate[296]: create BlkDrvUdp(prio:95,interval:0us,stacksize:131072)
    SysTaskFrame[230]: BlkDrvTcp(tid:486,OSprio:0) running
    SysTaskFrame[230]: BlkDrvUdp(tid:487,OSprio:0) running
    SysTaskCreate[296]: create OPCUAServer(prio:128,interval:0us,stacksize:131072)
    SysTaskCreate[296]: create GwCommDrvTcp(prio:95,interval:0us,stacksize:131072)
    SysTaskFrame[230]: OPCUAServer(tid:488,OSprio:0) running
    1452182088: Cmp=CM, Class=1, Error=0, Info=4, pszInfo= CODESYS Control V3
    1452182088: Cmp=CM, Class=1, Error=0, Info=5, pszInfo= Copyright (c) 3S - Smart Software Solutions GmbH
    1452182088: Cmp=CM, Class=1, Error=0, Info=6, pszInfo= <version>3.5.8.0</version> <builddate>Dec 8 2015</builddate>
    SysTaskFrame[230]: GwCommDrvTcp(tid:489,OSprio:0) running
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CM</cmp>, < id>0x00000001 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CmpMemPool< /cmp>, <id>0x0000001e</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CmpLog</cmp>, <id>0x00000013</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>CmpSettings </cmp>, <id>0x0000001a</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysFile, <id>0x00000104</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysCpuHandl ing</cmp>, <id>0x00000101</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>_, <id>0x00000103</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysMem</cmp>, <id>0x00000108</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysOut</cmp>, <id>0x0000010b</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysModule, <id>0x00000109</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysCom</cmp>, <id>0x00000100</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysDir</cmp>, <id>0x0000011b</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysEvent, <id>0x00000102</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysInternal Lib</cmp>, <id>0x00000107</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSem</cmp>, <id>0x0000010f</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSocket, <id>0x00000111</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTarget, <id>0x00000112</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTask, <id>0x00000114</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTime, <id>0x00000115</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTimeRtc< /cmp>, <id>0x00000127</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysTimer, <id>0x00000116</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysFileStre am</cmp>, <id>0x00000120</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysShm</cmp>, <id>0x00000110</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysMsgQ, <id>0x0000010a</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSemProce ss</cmp>, <id>0x00000119</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysEthernet </cmp>, <id>0x0000011c</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysMutex, <id>0x0000013a</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysSemCount </cmp>, <id>0x00000139</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= System: <cmp>SysProcess< /cmp>, <id>0x0000010e</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpApp</cmp>, <id>0 x00000002</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAppBP</cmp>, <id>0x00000073</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAppForce</cmp>, <id>0x00000074</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAsyncMgr</cmp>, <id>0x0000005f</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChecksum</cmp>, <id>0x0000000b</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpDevice</cmp>, 0x0000000e <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpEventMgr</cmp>, <id>0x0000005b</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpFileTransfer, <id>0x0000005e</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIecStringUtils, <id>0x0000007f</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIecTask</cmp>, < id>0x00000011 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpMonitor</cmp>, < id>0x00000014 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpMonitor2</cmp>, <id>0x00000032</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIoDrvC</cmp>, 0x00000066 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIoDrvIec</cmp>, <id>0x0000005a</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIoMgr</cmp>, <id>0x00000012</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpRetain</cmp>, 0x00000017 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpRouter</cmp>, 0x00000018 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSchedule</cmp>, <id>0x00000019</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpSrv</cmp>, <id>0 x0000001c</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBlkDrvTcp</cmp>, <id>0x00000030</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBlkDrvUdp</cmp>, <id>0x00000007</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBinTagUtil</cmp> , <id>0x00000004</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelMgr</cmp> , <id>0x00000009</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelServer, <id>0x0000000a</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpNameServiceServe r</cmp>, <id>0x00000016</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCommunicationLib </cmp>, <id>0x0000000c</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCoreDump</cmp>, <id>0x00000083</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpIecVarAccess, <id>0x00000060</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpPlcShell</cmp>, <id>0x00000128</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpTraceMgr</cmp>, <id>0x00000070</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpNameServiceClien t</cmp>, <id>0x00000015</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelClient, <id>0x00000008</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAAsyncMan</cmp>, <id>0x00004007</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAABehaviourMode l</cmp>, <id>0x00004015</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAACallback</cmp>, <id>0x00004001</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAADTUtil</cmp>, <id>0x00004013</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAFile</cmp>, < id>0x00004008 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAMemBlockMan, <id>0x00004003</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAANetBaseServic es</cmp>, <id>0x00004018</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAARealTimeClock </cmp>, <id>0x00004014</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASegBufferMan< /cmp>, <id>0x00004019</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASerialCom, <id>0x00004012</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATick</cmp>, < id>0x00004009 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATickUtil</cmp>, <id>0x00004010</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATimer</cmp>, <id>0x00004016</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAATypes</cmp>, <id>0x00004006</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpChannelClientIec </cmp>, <id>0x0000005d</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpNameServiceClien tIec</cmp>, <id>0x0000011d</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBinTagUtilIec, <id>0x0000005c</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpUserDB</cmp>, 0x00000064 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpUserMgr</cmp>, < id>0x00000061 <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCryptMD5</cmp>, <id>0x0000006a</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCharDevice</cmp> , <id>0x00000300</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpRasPi</cmp>, <id>0x00000089</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpBitmapPool</cmp> , <id>0x00000050</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpDynamicText</cmp>, <id>0x00000051</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpVisuHandler</cmp>, <id>0x00000054</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpVisuServer</cmp> , <id>0x00000057</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpOPCUA</cmp>, <id>0x00000125</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpWebServer</cmp>, <id>0x00000071</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpWebServerHandler V3</cmp>, <id>0x00000072</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAAStorage</cmp> , <id>0x0000007e</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpAlarmManager, <id>0x0000007c</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpGateway</cmp>, < id>0x0000000f <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpGwCommDrvTcp, <id>0x00000010</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCodeMeter</cmp>, <id>0x0000007a</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASdoClient, <id>0x00004011</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAASdoServer, <id>0x00004017</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpCAACanL2</cmp>, <id>0x00004004</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= <cmp>CmpEL6751CanDrv, <id>0x00005f0b</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= Dynamic: <cmp>CmpOpenSSL </cmp>, <id>0x00000033</id> <ver>3.5.8.0</ver>
    1452182088: Cmp=CM, Class=1, Error=0, Info=10, pszInfo= Dynamic: <cmp>CmpSocketC anDrv</cmp>, <id>0x00005f0d</id> <ver>3.5.8.0</ver>
    1452182089: Cmp=CM, Class=16, Error=0, Info=24, pszInfo= Call CH_INIT...
    1452182089: Cmp=SysFile, Class=1, Error=0, Info=1, pszInfo= PlcLogicPrefix=0: Ex ecute online command ResetOrginDevice to enable backup/restore feature
    1452182089: Cmp=CmpRouter, Class=16, Error=0, Info=19, pszInfo= <instances>7 router instances configured, first parallel router offset <offset>8
    1452182089: Cmp=CM, Class=16, Error=0, Info=25, pszInfo= CH_INIT done
    1452182089: Cmp=CM, Class=16, Error=0, Info=26, pszInfo= Call CH_INIT2...
    1452182089: Cmp=CmpBlkDrvUdp, Class=1, Error=0, Info=6, pszInfo= Network interfa ce: <ipaddress>127.0.0.1</ipaddress>, subnetmask <subnetmask>255.255.255.0
    1452182089: Cmp=CmpRouter, Class=1, Error=0, Info=4, pszInfo= Network interface <interface>ether local</interface> at router <instance>0</instance> registered
    1452182089: Cmp=CmpChannelMgr, Class=1, Error=0, Info=2, pszInfo= Running as net work server
    1452182089: Cmp=CmpChannelMgr, Class=1, Error=0, Info=1, pszInfo= Running as net work client
    1452182089: Cmp=CmpChannelServer, Class=1, Error=0, Info=0, pszInfo= <numofchann els="">4 channels available, each of the size <buffersize>100000 Bytes
    1452182089: Cmp=CM, Class=16, Error=0, Info=27, pszInfo= CH_INIT2 done
    1452182089: Cmp=CM, Class=16, Error=0, Info=47, pszInfo= Call CH_INIT201...
    1452182089: Cmp=CM, Class=16, Error=0, Info=48, pszInfo= CH_INIT201 done
    1452182089: Cmp=CM, Class=16, Error=0, Info=28, pszInfo= Call CH_INIT3...
    1452182089: Cmp=CmpBlkDrvTcp, Class=1, Error=0, Info=6, pszInfo= Local network a ddress: <ipaddress>127.0.0.1</ipaddress>
    1452182089: Cmp=CmpRouter, Class=1, Error=0, Info=4, pszInfo= Network interface <interface>BlkDrvTcp</interface> at router <instance>1</instance> registered
    1452182089: Cmp=CmpCodeMeter, Class=16, Error=0, Info=0, pszInfo= WIBU CmCompact version: 1.7.3391.0 - Build=2.4.2015
    1452182089: Cmp=CmpCodeMeter, Class=16, Error=0, Info=0, pszInfo= --- CodeMeter detected [0]: SN=32767--269967677, Version=1.18, Chip=0, Rev=0
    1452182089: Cmp=CmpCodeMeter, Class=16, Error=0, Info=0, pszInfo= [0] - Firm Code=0, ProductCode=0
    1452182089: Cmp=CmpCodeMeter, Class=16, Error=0, Info=0, pszInfo= [1] - () Firm Code=5000304, ProductCode=0, Features: 0x0
    1452182089: Cmp=CmpCodeMeter, Class=16, Error=0, Info=0, pszInfo= [2] - (
    1452182089: Cmp=CM, Class=16, Error=0, Info=29, pszInfo= CH_INIT3 done
    1452182089: Cmp=CM, Class=16, Error=0, Info=74, pszInfo= Call CH_INIT_SYSTEM_TAS KS...
    1452182089: Cmp=CM, Class=16, Error=0, Info=75, pszInfo= CH_INIT_SYSTEM_TASKS do ne
    1452182089: Cmp=CM, Class=16, Error=0, Info=30, pszInfo= Call CH_INIT_TASKS...
    1452182089: Cmp=CmpApp, Class=16, Error=0, Info=0, pszInfo= Allocate area: app=A pplication, area=0, size=1048576, type=0xfedf, addr=0x0x76a44000
    1452182089: Cmp=CM, Class=16, Error=0, Info=10, pszInfo= IEC|Dynamic: <cmp>Onlin eLicenseManager</cmp>, <id>0x0000100d</id> <ver>3.5.8.0</ver>
    1452182089: Cmp=CmpOPCUA, Class=1, Error=0, Info=0, pszInfo= Valid license found for OPC UA server.
    1452182089: Cmp=CmpApp, Class=1, Error=0, Info=22, pszInfo= No retain area in bo otproject of application [<app>Application</app>]
    1452182089: Cmp=CmpApp, Class=1, Error=0, Info=6, pszInfo= Bootproject of applic ation [<app>Application</app>] loaded
    1452182089: Cmp=CmpApp, Class=16, Error=0, Info=3, pszInfo= application=<app>App lication</app>, codeid=<codeid>{5440b0f3-00000000-00000000-00000000}</codeid>
    1452182089: Cmp=CmpApp, Class=16, Error=0, Info=4, pszInfo= application=<app>App lication</app>, dataid=<dataid>{41454f1b-00000000-00000000-00000000}</dataid>
    1452182089: Cmp=CmpRouter, Class=1, Error=0, Info=1, pszInfo= Setting router <in stance="">0 address to </in></buffersize></numofchann></subnetmask></offset></instances></cmp></cmp></cmp></cmp></cmp>
    </cmp></cmp></cmp></cmp></cmp></cmp></cmp>
    </cmp></cmp>
    </cmp></cmp></cmp></cmp></cmp></cmp></cmp></cmp></cmp></cmp></cmp></cmp></cmp></cmp>
    (0001)
    1452182089: Cmp=CmpRouter, Class=1, Error=0, Info=1, pszInfo= Setting router <in stance="">1 address to
    (2ddc:7f00:0001)
    1452182089: Cmp=CM, Class=16, Error=0, Info=31, pszInfo= CH_INIT_TASKS done
    1452182089: Cmp=CM, Class=16, Error=0, Info=32, pszInfo= Call CH_INIT_COMM...
    1452182089: Cmp=CmpOPCUA, Class=1, Error=0, Info=0, pszInfo= *** *******
    1452182089: Cmp=CmpOPCUA, Class=1, Error=0, Info=0, pszInfo= OPC UA S erver
    1452182089: Cmp=CmpOPCUA, Class=1, Error=0, Info=0, pszInfo= URL: opc.tcp: //raspberrypi:4840
    1452182089: Cmp=CmpOPCUA, Class=1, Error=0, Info=0, pszInfo= URL: opc.tcp: //127.0.0.1:4840
    1452182089: Cmp=CM, Class=16, Error=0, Info=33, pszInfo= CH_INIT_COMM done
    1452182089: Cmp=CM, Class=16, Error=0, Info=32, pszInfo= Call CH_INIT_FINISHED.. .
    1452182089: Cmp=CmpApp, Class=1, Error=0, Info=10, pszInfo= Application [<app>Ap plication</app>] started
    1452182089: Cmp=CM, Class=16, Error=0, Info=33, pszInfo= CH_INIT_FINISHED done
    1452182089: Cmp=CM, Class=1, Error=0, Info=34, pszInfo= CODESYS Control ready
    Runtime received SIGSEGV (address: 0x18 reason: address not mapped to object)
    handleException[79]: getting the context...
    1452182099: Cmp=CmpRouter, Class=1, Error=0, Info=5, pszInfo= Network interface <interface>ether local</interface> unregistered
    1452182099: Cmp=CmpBlkDrvUdp, Class=1, Error=0, Info=6, pszInfo= Network interfa ce: <ipaddress>10.0.0.132</ipaddress>, subnetmask <subnetmask>255.255p
    </subnetmask></in>
    Related
    Talk.ru: 1
    Talk.ru: 2
  • Moderator3S
    Moderator3S - 2016-01-07
    hi,
    hm strange,
    could you please remote the application and restart teh runtime?
    sudo -s
    rm /root/App*
    /etc/init.d/codesyscontrol stop
    /etc/init.d/coidesyscontrol start
    then check if a new download lead to the same problem.
    If yes we need the projectarchive.
    Moderator3S
    I did as you suggest. Trying to go online again there is not program loaded (correct).
    Then rebuild->online..the same. Stay stopped..
    where can i send the archive?
    I sent the archive.. Thanks in advance for any help
    if I remove the
    [SysCom]
    Linux.Devicefile=/dev/ttyUSB
    portnum := COM.SysCom.SYS_COMPORT1;
    and reboot, then runtime get back running (without any RTU capability of course..)
    eschwellinger - 2016-01-08
    this is a bug.
    Workaround is to use:
    3.5.5.0 library
    This will be fixed hopefully a.s.a.p
    IMG: ModbusRTU3.5.5.0.jpg
  • hki75 - 2016-01-08
    Thanks a lot for your help Edwin!