I've managed to map the I/O for an eDAM-5029 unit. However, I'm having trouble replicating a function code 4 & function code 6 command structure for the ADAM-6066.
Here's how I did it for the eDAM-5029 unit:
If you have any idea as to what I should put for the offset and I/O mapping values that would be fantastic as I've been biting my nails over it.
Hi guys,
I've managed to map the I/O for an eDAM-5029 unit. However, I'm having trouble replicating a function code 4 & function code 6 command structure for the ADAM-6066.
Here's how I did it for the eDAM-5029 unit:
If you have any idea as to what I should put for the offset and I/O mapping values that would be fantastic as I've been biting my nails over it.
Here's the manual for the ADAM-6000 series.
The MODBUS mapping datasheet for ADAM-6066 is on document page 233-34.
http://downloadt.advantech.com/ProductF ... al_Ed5.pdf
Many thanks.
Hi,
On EDAM-5029 you used function 03 and 04. On ADAM-6066 you have to use functions 02 for DI and 05/15 for DO.
Try this configuration:
BR
Zdenko.
You sir, are a gent and scholar!
Cheers man.