Welcome to our new forum
All users of the legacy CODESYS Forums, please create a new account at account.codesys.com. But make sure to use the same E-Mail address as in the old Forum. Then your posts will be matched.
Close
I did some measuring with the meter, and the sensor is indeed putting out 4-20ma. I also checked voltage, and the sensor outputs between 1.55 volts (when the sensor is putting out 4ma) and 4.55 volts (when the sensor is putting out 12ma). The voltage remains the same at 4.55 volts from 12-20ma.
The code is very simple, using an IFM library block:
VAR_INPUT
 xChannelNumber:BYTE;(*Channel number for the X angle*)END_VARVAR
 xInputAnalogBlockExtended:INPUT_ANALOG_E;    (*Input block for extended input, X*)
 xTempWord:WORD;
 xError:BYTE;END_VARxInputAnalogBlockExtended(
    ENABLE:=TRUE,
    MODE:=IN_CURRENT,    (*Globalconstantdefinedinlibrary*)
    CHANNEL:=xChannelNumber, (*Integerinput*)
    OUT=>xTempWord,
    ERROR=>xError);
Any ideas?
Thanks!
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi everyone,
I've attached a 4-20ma level sensor to a PLC input that is configured for current. The PLC reads the range 4-12ma just fine, but anything from 12-20ma is just read as 12ma by the PLC. I'm using an IFM CR0232 (http://www.ifm.com/products/ca/ds/CR0232.htm) with Codesys 2.3, and the sensor is a Turck Inclinometer (http://old.turck.us/illustrations/M1...0(sheet_1.pdf).
I did some measuring with the meter, and the sensor is indeed putting out 4-20ma. I also checked voltage, and the sensor outputs between 1.55 volts (when the sensor is putting out 4ma) and 4.55 volts (when the sensor is putting out 12ma). The voltage remains the same at 4.55 volts from 12-20ma.
The code is very simple, using an IFM library block:
Any ideas?
Thanks!
as you can see in PLCS.net it is a hardware problem, as the sensor is not able to send a signal above 4 volts (strange but cheaper.
Yep, it was a hardware issue. The PLC input had a resistance that was too high for the sensor.