    Hello everyone, i'm using PID_FIXCYCLE just with P and I.
    I need sometime to disable the I part : if i put TN=0 and i use only TP, the output of PID remains blocked.
    Where i'm wrong ?

     
  • shooter - 2015-04-03

    fix is same as pid however you need to give a time to calculate (that can be different from realtime)
    if only using P check the PB(or Kp)

     
  • MuhteremCayli - 2015-04-08

    Integral effect in the formula is like 1/TN so if you give "0" to TN a math error occur.
    So if you want to decrease the effect of Integral give bigger value.

     
  • shooter - 2015-04-08

    math error is not occuring as it is checked in integral. and on other places when using util.lib
    same for oscat.lib btw.
    so if set to zero it is discarded.

     