Performance test

astrand
2013-11-08
2013-11-19
  • astrand - 2013-11-08

    Hi! I want to know how long different operations take. To find out, I've written a small performance test which executes different statements multiple times, and then checks how long the execution took. It works quite fine in simulation mode, with 50000 loops of each statement.

    On real hardware, however, it does not: As soon as I go over ~200 loops, Codesys online communication will stop. This was expected, but what is strange is that you cannot go online even after the performance test is done, ie when the cycle time is good again. So either the runtime gets stuck in some strange error state, or it crashes altogether. If anyone has a clue of why this happens, or want to improve on the performance test in general, I'd be happy. Code will follow in comment, since the board does not allow attachements. (Why?)

     
  • astrand - 2013-11-08

    perftest.exp:

    ( @NESTEDCOMMENTS := 'Yes' )
    ( @PATH := '' )
    ( @OBJECTFLAGS := '0, 8' )
    ( @SYMFILEFLAGS := '2048' )
    FUNCTION_BLOCK DummyFB
    VAR_INPUT
    invar: BOOL;
    END_VAR
    VAR_OUTPUT
    outvar: BOOL;
    END_VAR
    VAR
    END_VAR
    ( @END_DECLARATION := '0' )
    outvar := invar;
    END_FUNCTION_BLOCK

    ( @NESTEDCOMMENTS := 'Yes' )
    ( @PATH := '' )
    ( @OBJECTFLAGS := '0, 8' )
    ( @SYMFILEFLAGS := '2048' )
    FUNCTION DummyFunc : BOOL
    VAR_INPUT
    END_VAR
    VAR
    END_VAR
    ( @END_DECLARATION := '0' )
    DummyFunc := TRUE;
    END_FUNCTION

    ( @NESTEDCOMMENTS := 'Yes' )
    ( @PATH := '' )
    ( @OBJECTFLAGS := '0, 8' )
    ( @SYMFILEFLAGS := '2048' )
    FUNCTION NanoSecsSince : DWORD
    VAR_INPUT
    start: TIME;
    END_VAR
    VAR
    END_VAR
    ( @END_DECLARATION := '0' )
    NanoSecsSince := TIME_TO_DWORD(TIME() - start) * 1000000;
    END_FUNCTION

    ( @NESTEDCOMMENTS := 'Yes' )
    ( @PATH := '' )
    ( @OBJECTFLAGS := '0, 8' )
    ( @SYMFILEFLAGS := '2048' )
    PROGRAM PLC_PRG
    VAR CONSTANT
    MAXLOOPS: DWORD := 50000;
    END_VAR
    VAR
    loops: DWORD;
    state: BYTE;
    x: DWORD;
    start: TIME;
    cycletime: TIME;
    nanosecs: DWORD;

    my_fb: DummyFB;
    my_byte: BYTE;
    my_int: INT;
    my_word: WORD;
    my_real: REAL;
    my_short_str: STRING := 'ab';
    my_long_str: STRING(255) := '01234567890abcdef01234567890abcdef01234567890abcdef01234567890abcdef01234567890abcdef01234567890abcdef01234567890abcdef01234567890abcdef01234567890abcdef01234567890abcdef';
    my_2d_array: ARRAY[0..7] OF INT := 0, 1, 2, 3, 4, 5, 6, 7;
    my_ton: TON;
    
    (* Results *)
    for_loop: DWORD;
    function_call: DWORD;
    fb_call: DWORD;
    int_div: DWORD;
    float_div: DWORD;
    str_len_short: DWORD;
    str_len_long: DWORD;
    array_index: DWORD;
    timer_call: DWORD;
    

    END_VAR

    ( @END_DECLARATION := '0' )
    start := TIME();

    IF state = 0 THEN
    loops := MAXLOOPS;
    END_IF

    FOR x := 1 TO loops DO
    CASE state OF

    (* First 10 cycles are warmup *)
    0:
        for_loop := 0;
    
    10: (* Measured no-op - for_loop*)
        ;
    
    21: (* function_call *)
        DummyFunc();
    
    22: (* fb_call *)
        my_fb(invar := TRUE);
    
    30: (* int_div *)
        my_word := 4711 / 17;
    
    31: (* float_div *)
        my_real := 4711.1 / 17.1;
    
    40: (* str_len_short *)
        my_int := LEN(my_short_str);
    
    41: (* str_len_long *)
        my_int := LEN(my_long_str);
    
    50: (* array_index *)
        my_int := my_2d_array[4];
    
    60: (* timer_call *)
        my_ton(IN:= TRUE, PT:= T#1h);
    
    100: (* stop test *)
        loops := 0;
    
    END_CASE;
    

    END_FOR

    IF loops > 0 THEN
    nanosecs := NanoSecsSince(start) / LOOPS - for_loop;

    CASE state OF
    
    10: (* Measured no-op *)
        for_loop := nanosecs;
    
    21:
        function_call := nanosecs;
    
    22:
        fb_call := nanosecs;
    
    30:
        int_div := nanosecs;
    
    31:
        float_div := nanosecs;
    
    40:
        str_len_short := nanosecs;
    
    41:
        str_len_long := nanosecs;
    
    50:
        array_index := nanosecs;
    
    60:
        timer_call := nanosecs;
    
    END_CASE;
    
    state := state + 1;
    

    END_IF

    cycletime := TIME() - start;

    END_PROGRAM

    ( @NESTEDCOMMENTS := 'Yes' )
    ( @GLOBAL_VARIABLE_LIST := 'Global_Variables' )
    ( @PATH := '' )
    ( @OBJECTFLAGS := '0, 8' )
    ( @SYMFILEFLAGS := '2048' )
    VAR_GLOBAL
    END_VAR

    ( @OBJECT_END := 'Global_Variables' )
    ( @CONNECTIONS := Global_Variables
    FILENAME : ''
    FILETIME : 0
    EXPORT : 0
    NUMOFCONNECTIONS : 0
    )

    ( @NESTEDCOMMENTS := 'Yes' )
    ( @GLOBAL_VARIABLE_LIST := 'Variable_Configuration' )
    ( @PATH := '' )
    ( @OBJECTFLAGS := '0, 8' )
    ( @SYMFILEFLAGS := '2048' )
    VAR_CONFIG
    END_VAR

    ( @OBJECT_END := 'Variable_Configuration' )
    ( @CONNECTIONS := Variable_Configuration
    FILENAME : ''
    FILETIME : 0
    EXPORT : 0
    NUMOFCONNECTIONS : 0
    )

    _ALARMCONFIG
    _ALARMCONFIGNEXTTEXTID : 10002
    _ALARMCONFIGFORMATS : 'HH$':$'mm$':$'ss','dd$'-$'MM$'-$'yyyy'
    _ALARMCLASSLIST : 1
    _ALARMCLASSID : 0
    _ALARMCLASSACKTYPE : 0
    _ALARMCLASSNAME : 'DEFAULT'
    _ALARMCLASSDESCRIPTION : ''
    _ALARMCLASSBGCOLORS : 16777215,16777215,16777215
    _ALARMCLASSTEXTCOLORS : 3394560,255,16711680
    _ALARMCLASSBITMAPS : '','',''
    _ALARMACTIONLIST : 0
    ( @ALARMCLASSRESETCOLORS := '_ALARMCLASSRESETCOLORS: 33023,16777215' )
    ( @ALARMCLASSRESETBITMAP := '_ALARMCLASSRESETBITMAP: $'$'' )
    _ALARMGROUPLISTNAME : 'System'
    _ALARMGROUPPATH : 'System'
    _ALARMGROUPLIST : 0
    _VISUALSETTINGSFLAGS : 0,0,0,0
    _VISUALSETTINGSFLAGS : '','',''
    _VISUALSETTINGSDYNTEXTFILECOUNT : 0

    ( @ALARMCONFIGFLAGS := '_ALARMCONFIGFLAGS: 4' )
    ( @ALARMCONFIGGLOBALDB_STR := '_ALARMCONFIGGLOBALDB_STRINGS: $'$',$'$',$'$',$'$'' )
    ( @ALARMCONFIGGLOBALDB_NUM := '_ALARMCONFIGGLOBALDB_NUMBERS: 0,0' )
    _END_ALARMCONFIG

    LIBRARY
    STANDARD.LIB 4.10.05 11:14:46
    ( @LIBRARYSYMFILEINFO := '0' )
    NumOfPOUs: 21
    CONCAT: 0
    CTD: 0
    CTU: 0
    CTUD: 0
    DELETE: 0
    F_TRIG: 0
    FIND: 0
    INSERT: 0
    LEFT: 0
    LEN: 0
    MID: 0
    R_TRIG: 0
    REPLACE: 0
    RIGHT: 0
    RS: 0
    RTC: 0
    SEMA: 0
    SR: 0
    TOF: 0
    TON: 0
    TP: 0
    NumOfGVLs: 0
    END_LIBRARY

    PLC_CONFIGURATION
    _GLOBAL
    _VERSION: 3
    _AUTOADR: 1
    _CHECKADR: 1
    _SAVECONFIGFILESINPROJECT: 0
    _END_GLOBAL

    _MODULE: '3S'
    _SECTION_NAME: 'not_found'
    _INDEX_IN_PARENT: '-1'
    _MODULE_NAME: 'not_found'
    _NODE_ID: 0
    _IECIN: %IB0
    _IECOUT: %QB0
    _IECDIAG: %MB0
    _DOWNLOAD: 1
    _EXCLUDEFROMAUTOADR: 0
    _COMMENT: ''
    _END_MODULE
    PLC_END

    RESOURCE

    END_RESOURCE

    _WORKSPACE
    _GLOBALVISUALSETTINGS
    _VISUALSETTINGSFLAGS : 0,0,0,0
    _VISUALSETTINGSFLAGS : '','',''
    _VISUALSETTINGSDYNTEXTFILECOUNT : 0
    _VISUALBITMAPLISTCOUNT : 0
    _END_GLOBALVISUALSETTINGS
    _END_WORKSPACE

    MACRO
    MacroName: 'export'
    MacroMenu: '&export'
    MacroCmd: 'query off ok'
    MacroCmd: 'project export project.exp'
    MacroCmd: ''
    END_MACRO

     
  • shooter - 2013-11-18

    your loops are taking too long, so the PLC will have a watchdog alarm and resets and starts all over when nothing is done to prevent ths.

    In ST you have to make sure the program is completed in watchdog time
    As with most machines you will not get a good answer to this as a PLC needs time to update i/o and communication etc.
    the time is updated via a counter internal, so it will be on time

    by the way if you mul by 1000000 you do not get a better result as it is a DWORD. just leave it like it is.
    you will have to break up your program in subs

     
  • astrand - 2013-11-19

    shooter hat geschrieben:
    your loops are taking too long, so the PLC will have a watchdog alarm and resets and starts all over when nothing is done to prevent ths.
    In ST you have to make sure the program is completed in watchdog time
    As with most machines you will not get a good answer to this as a PLC needs time to update i/o and communication etc.
    the time is updated via a counter internal, so it will be on time

    The cycle time is not very long, about 2000 us. I have other programs running on the same device with such cycle time without problems. It must be something more to this problem.

     