I am attempting to communicate between a RedLion touch panel (G308C2) and a Wago 882 via Modbus-RTU.
The touch panel is the master and the PLC the slave (via a 750-653 Modbus card).
Communications is established using the Wago TerminalSlave.lib library and its TERMINAL_MODBUSSLAVE_RTU function block in CoDesSys.
Now to the question ,
I have established communications but even with the most trivial of applications I receive an error code from the bERROR output, "INVALID: 204" which I cannot identify in documentation or google.
I realise that this a bit obscure but if anyone has any ideas I would appreciate it.
Kind regards,
Alex.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I take a look at the Wago docs.. just 0-1-2-3 error codes are foreseen..I used same block some months ago with 758 IPC..I used this settings and it was good:
Hi All,
I am attempting to communicate between a RedLion touch panel (G308C2) and a Wago 882 via Modbus-RTU.
The touch panel is the master and the PLC the slave (via a 750-653 Modbus card).
Communications is established using the Wago TerminalSlave.lib library and its TERMINAL_MODBUSSLAVE_RTU function block in CoDesSys.
Now to the question ,
I have established communications but even with the most trivial of applications I receive an error code from the bERROR output, "INVALID: 204" which I cannot identify in documentation or google.
I realise that this a bit obscure but if anyone has any ideas I would appreciate it.
Kind regards,
Alex.
I take a look at the Wago docs.. just 0-1-2-3 error codes are foreseen..I used same block some months ago with 758 IPC..I used this settings and it was good:
RTUClient(
EN:=TRUE ,
bSLAVE_ADDRESS:=104 ,
bCOM_PORT:=2,
cbCOM_BAUDRATE:= 3840,
cpCOM_PARITY:=0 ,
csCOM_STOPBITS:= 1,
cbsCOM_BYTESIZE:=8 ,
cfCOM_FLOW_CONTROL:= 4, ( 0=no flow control; 1=XON-XOFF 2=RTS-CTS 3=full duplex ; 4=half duplex )
tTIME_OUT:= ,
iBIT_OFFSET:=,
tWATCHDOG_TIME:= ,
aDATA:=ModbData ,
xWATCHDOG_OK=> ,
bERROR=> );
and call this PRG as fast as possible in a dedicate task(freewheeling) otherwise I get comm very bad and slow.. try this...