[quote="Dutch"]Have been trying unsuccessfully to have CoDeSys create a "Remote" Connection.
Wago 750-882 PFC
Sierra Wireless Raven 3G cell router.
Remote connections to 2 Access Points and Camera all work marvelously.
CoDeSys will not connect.
ie. The PLC is 300 miles away on a client's network and I want to change some code.
I go to Online>Communication Parameters; give it the correct IP Address. The Port Forwarding in the remote router is correct: Port 2455>>192.168.1.25
I changed the download timeout to 100000 ms.
All I ever get is Communication Error, #0, Logout Performed.
OK, fair enough, then I try to change the Gateway. All I ever get is " No Gateway with that address found"
Can anyone elaborate on what the setting for "Gateway" should be?
Thank you in advance.
Dutch
dutch@wiredboat.com778-991-8360[/quote]
Gateway have to be "Local", then in "Communication Parameters" -> "New" choose "TCP/IP" -> OK. Then you have to enter IP in "address" field (real IP of remote router WAN/Internet port) or hostname (in case of e.g. dyndns usage), port ....I think you know what else