CANopen communication with a Sick barcode scanner

swtroelofs
2012-01-10
2014-07-07
  • swtroelofs - 2012-01-10

    Hello everybody,

    I am having some issues communicating with a barcode scanner from Sick through CANopen. Does anybody have any experience with this device?

    This is what already works:
    I have installed the EDS file and added the scanner to my PLC configuration. Then I mapped several values to PDO's.
    Now when I write a value to the scanner I get the correct response back with the current barcode being red.

    So far so good, but:
    Now I want to get the read data from the scanner with a SDO packet.
    Does anyone know how I can make the scanner upload the read results by SDO?
    The reading result should be located at address 0x2000.

    Can anyone point me in the right direction?
    Thanks,
    Stefan Roelofs

     
  • swtroelofs - 2012-02-14

    I got it working eventually.
    If anyone needs some advise on this let me know.

    Stefan

     
  • ErikS - 2012-03-26

    Hello Stefan,

    i'm currently stuck with a similar problem.
    A CLV431 transmits data through PDOs (e.g. "length of datastring", "type of datastring") but the result string array is always empty.

    Can you please give me a hint where to look into?

    Thank you!
    Erik

    PLC: Moeller XC-CPU101-C128k
    Scanner: Sick CLV431-2010

     
  • swtroelofs - 2012-03-27

    Hi Erik,

    I eventually used the function: CanOpenSendSDO (from the libary: 3S_CANopenManager)

    With the following parameters:

       sdoTransfer         : CanOpenSendSDO;
       xSdoEnable            : BOOL;
       aSdoDataBuffer         : ARRAY[0..99] OF BYTE;
       aSdoAnswerBytes       : ARRAY[0..7] OF BYTE;
       iSdoAnswerLength      : INT;
       xSdoWaitForAnswer      : BOOL;
       xSdoAnswerRec          : BOOL;
       xSdoToggleUnequal      : BOOL;
       xSdoAbortRec         : BOOL;
       aSdoAbortRec         : ARRAY[0..3] OF BYTE;
    
    (*Do not call this FB while the targetnode is not in state 5.*)
    (*Create an instance within your application for the FB, one for each node you want to communicate at the same time.*)
    (*There are maximum 64 instances possible.*)
    (*Do not change inputparameters, while the FB is waiting for an answer.*)
    sdoTransfer(
       Enable         := xSdoEnable,      (*Change from 0->1 will start the transmission.*)
       wDrvNr         := WORD#0,            (*Index of CanMaster, that will send the message. 0 if only one exists*)
       ucNodeId      := BYTE#9,            (*NodeId of targetnode.*)
       wIndex         := 16#2000,         (*Index of ObjectDict.-entry*)
       bySubIndex      := 16#04,         (*SubIndex within the index.*)
       ucModus         := 16#40,         (*SDO-mode, use 16#40 for read-request, use 16#23 for 4-byte-write-request.
                                                                   use 16#27 for 3-byte...
                                                                  use 16#2B for 2-byte...
                                                                  use 16#2F for 1-byte...
                                                            use 16#21 for downloading more than 4 bytes using the segmented transfer.*)
       ucByte0         := 0,            (*The 4 possible databytes.(That's why the FB is called ...light*)
       ucByte1         := ,
       ucByte2         := ,
       ucByte3         := ,
       aAbortCode      := ,
       (*Additional functionality if the segmented transfer should be used.*)
       (*For this mode, use 16#41, 16#40 as an read-request and 16#21 as a write request.
        In this case the following DataLength parameter and DataBuffer-address is used.*)
       dwDataBufferLength:= DWORD#99,
       pDataBuffer      := ADR(aSdoDataBuffer),      (* <--- Output is here *)
       bWaitForAnswer   => xSdoWaitForAnswer,
       bAnswerRec      => xSdoAnswerRec,
       (*The following are written by the CanOpenInterfaceMan.*)
       ucAnswerBytes   => aSdoAnswerBytes,
       iAnswerLength   => iSdoAnswerLength,
       bToggleUnequal   => xSdoToggleUnequal,
       bAbortRec      => xSdoAbortRec,
       aAbortRec      => aSdoAbortRec);
    

    First set an output (over PDO) to the scanner so it starts to scan for a new barcode.
    Next check if a counter (over PDO) is increased (counter will increase for each read result)
    Now set 'xSdoEnable'
    Wait for 'xSdoAnswerRec' is TRUE
    The array aSdoDataBuffer now contains the Read Data.

    I have attached a CANopen manual. Maybe it helps you.

    By the way: I used a Sick CLV650 scanner.

    Manual_CANopen_IDpro_V15.pdf [191.89 KiB]

     
  • ErikS - 2012-03-30

    Hi Stefan,

    thank you very much for your help, you saved me a lot of time!

    By now I got the CLV up and running. The point was "SDO-Transfer" - I always tried PDO-Transfer, which isn't supported by the CLV43x series...
    Especially the manual was helpful, because it contains information about the CAN-messages used by SICK. So I was able to monitor communication between CLV and the PLC with a CAN-Sniffer.

    Best regards
    Erik

     
  • alex87 - 2014-07-04

    Hello!

    I'm using your code for recieving SDO "swtroelofs". In CANopen analyzer the remote node/device answer read-Request for SDO, but my BUFFER is empty. Do not have a clue why the buffers are empty?

    Another interesting thing is that, when the state of xSDOenable goes from TRUE to FALSE. I got Abort code 0 object SSDO, answer from remote node

    There is a picture attached.

    Thnx in advance,
    Alex

    IMG: SDO_recieve_problem.PNG

     
  • alex87 - 2014-07-07

    No one? I really do not know where to search the answer...

    please help

    regards,
    Alex

     
  • alex87 - 2014-07-07

    Solved!

    I call a FB within PLC_PRG when device state is 5. And the most important I wait for bWaitForAnswer and then xSDOenable=FALSE. I got no error in Analyser.

    The data is not in aSDOdataBuffer but in ucAnswerBytes:ARRAY[0..7] OF BYTE. Last 4 BYTES (4..7) presents recieved SDO data.

    regards,
    Alex

     