Hello. I have difficulties to run the OPC server of my pigeon PLC (raspberry pi compute inside) with runtime 3.5.14.20.
The UaExpert windows "Add Server" : see attachment nΒ°3
The UaExpert windows error : see attachment nΒ°2
The Codesys log window: see attachment nΒ°1
I have a questions : 1) Which configuration file should I use?
"/etc/CODESYSControl_User.cfg" or "/etc/CODESYSControl.cfg"
2) What configuration in this file
[CmdOPCUA] NetworkAdapter = eth0 NetworkPort = 4840
OU
[CmpOPCUAServer] NetworkAdapter=eth0 NetworkPort=4840
3) What means the errors in Codesys log and UaExpert log ?
Thank you
Note: When I do a Codesys Win V3 project, everything works.
Hi. I found the solution.
In UaExpert OPC client, after add the server, display the properties of this server and replace the "EndPoint URL" :
by
Now, it works
Log in to post a comment.