Codesys Profinet Controller - Codesys Profinet Device Communication

Batinic911
2019-04-02
2019-04-04
  • Batinic911 - 2019-04-02

    Hallo zusammen,

    Ist es mΓΆglich eine Kommunikation zwischen einen Codesys Profinet Controller (Windows 10 Codesys Control Win 64) und Codesys Profinet Device (Windows 7 Codesys Control Win 64) ohne die jeweiligen Lizenzen in Demo Version zu testen. Wo kann man Beispiele finden?

    Mit freundlichen Grüßen

    Hello everybody,

    Is it possible to test a communication between a Codesys Profinet Controller (Windows 10 Codesys Control Win 64) and Codesys Profinet Device (Windows 7 Codesys Control Win 64) without the respective licenses in demo version? Where can I find examples?

    Best regards

     
  • eschwellinger

    eschwellinger - 2019-04-02

    Hi,

    here in this Forum section is an example project for profinet with two Raspberry Pi's

    l viewtopic.php?f=23&t=6247&p=16870#p16870 l

    BR
    Edwin

     
  • Batinic911 - 2019-04-03

    Hello Edwin,

    unfortunately the profinet communication is not working.
    I have take the project with 2 raspberry pi.
    The part for profinet Controller I have loaded to Rasbery Pi (Bild 1-4).
    The part for profinet device I have loaded to Codesys Control Win X64 (Bild 5-7)(I have also a Codesys Profinet Device License on The Codesys Runtime key which is insertet to the Win 7 PC).
    Can you please tell me any sugestion what I m doing wrong.

    Do I have to do something with the license for Codesys Profinet Device on the Codesys Runtime Key or it is enough just to plug in the PC.

    Best regards

    IMG: Bild 7.png

    IMG: Bild 6.png

    IMG: Bild 5.png

    IMG: Bild 4.png

    IMG: Bild 3.png

    IMG: Bild 2.png

    IMG: Bild 1.png

     
  • dFx

    dFx - 2019-04-03

    Usually, when you declare a PN device with 8 in, 64 in/out, 8 out you have to declare the controler symetrically, communication wise. So 8 out, 64 in/out, 8 in.

    I don't know if this apply for codesys, but in siemens softs, it does.

     
  • eschwellinger

    eschwellinger - 2019-04-04

    Hi,
    winpcap is installed? ( this is mandatory for Control Win)
    For a test I would recommend to disable the firewall
    then try to scan the pn device from the pn controller application.
    Send/attach the screenshots and plclogger of that.

    BR
    Edwin

     
  • Batinic911 - 2019-04-04

    Hello Edwin,

    attached the screenshots.

    Best regards

    IMG: Bild 1.png

    IMG: Bild 2.png

    IMG: Bild 3.png

    IMG: Bild 4.png

     

Log in to post a comment.