Hi,
I am trying to communicate with a modbus slave device to read the floating point variable. In Codesys I can see only the option to read as a 16 bit word. How can i read the real value from my slave 32bit floating point variable. I face this problem both Modbus RTU and Modbus TCP
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Anonymous
-
2018-06-22
Originally created by: scott_cunningham
Modbus only supports WORD data transfer. You need to read two registers locations (2 words) and then convert your DWORD to REAL. You also may need to confirm the order of your words, too (upper/lower).