I'm trying to use the CIA405.SDO_WRITE4 function to write a SDO to a device. My issue is the index input (SDO_WRITE4.INDEX) is of type WORD but I am trying to write a SDO in the Manufacturer Specific range (ie index 16#5999). This index value is 4 bytes but a WORD is only 2.
Im getting SDO_WRITE4.ERRORINFO 101122066 or 0607 0012h which from the abort code represents: "Data type does not match; length of service parameter too high."
Any ideas? Is there another way to write higher indices SDO?
Thanks.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
It was en error to do with the data variable being written. With SDO_WRITE I needed to dynamically change WRITE_SDO.Datalength variable based on data type being transmitted.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I'm trying to use the CIA405.SDO_WRITE4 function to write a SDO to a device. My issue is the index input (SDO_WRITE4.INDEX) is of type WORD but I am trying to write a SDO in the Manufacturer Specific range (ie index 16#5999). This index value is 4 bytes but a WORD is only 2.
Im getting SDO_WRITE4.ERRORINFO 101122066 or 0607 0012h which from the abort code represents: "Data type does not match; length of service parameter too high."
Any ideas? Is there another way to write higher indices SDO?
Thanks.
An SDO message is 8 bytes in total:
1 for the command
2 for the index
1 for the sub-index
4 for the data bytes
The maximum value of a WORD is 16#FFFF, this means you can also access index 16#5999
The error is about the variable that you try to write, try with write8 or write2.
Enviat des del meu Aquaris M5.5 usant Tapatalk
Sorry. Via sdo you cant write an 8bytes message.
Try with write2 or write 1
Enviat des del meu Aquaris M5.5 usant Tapatalk
Thank you for the feedback.
It was en error to do with the data variable being written. With SDO_WRITE I needed to dynamically change WRITE_SDO.Datalength variable based on data type being transmitted.