PostPosted: Wed Apr 25, 2018 7:31 am 
Offline

Joined: Sun Dec 18, 2011 10:29 pm
Posts: 21
Hello,

after inserting the EL6900 module, the SafetyTask is not automatically added and, even from the context menu of the SafetyApp, it is not possible to add it: the selection is missing.
Any suggestion?

Thanks a lot in advance.


Top
   
PostPosted: Thu Apr 26, 2018 8:31 pm 
Offline
Site Admin

Joined: Mon Sep 05, 2005 9:42 am
Posts: 2892
Hi,
not sure what you are missing but are these the steps you are doing?
https://www.youtube.com/watch?v=y5c-ZxtCc0o

BR
Edwin


Top
   
PostPosted: Fri Apr 27, 2018 7:50 am 
Offline

Joined: Sun Dec 18, 2011 10:29 pm
Posts: 21
That's great, thanks.
The tutorial is very clear.

However I have an additional question: is it allowed to create safety FB's? I see in the POU tab the possibility to insert "External FB (EtherCAT Safety)". By trying to create a new FB, the declaration area is displayed only: no code is allowed to create.
Any suggestion?

Thanks a lot in advance.


Top
   
PostPosted: Tue Jul 10, 2018 1:16 pm 
Offline

Joined: Sun Dec 18, 2011 10:29 pm
Posts: 21
Hello,

what is the default pw the download the safety application?

Thanks a lot in advance.


Top
   
PostPosted: Tue Jul 10, 2018 2:06 pm 
Offline

Joined: Mon Nov 03, 2014 7:15 am
Posts: 32
Hi ugogiannotti!

As far as I know, the standard password for the EL6900 is "TwinSAFE".

You need to know the serial number of the module, which is written on the side...

Good luck!

Alfred


Top
   
PostPosted: Wed Jul 11, 2018 7:21 am 
Offline

Joined: Sun Dec 18, 2011 10:29 pm
Posts: 21
Hi alwoso,

thanks a lot. I also find the answer into the related Beckhoff manual.
I have one more question to post: any idea regarding the message I get when attemping to download the application to the safety module? Please, have a look to the attached file.

Thanks a lot in advance.

Attachment:
Immagine1.png


You do not have the required permissions to view the files attached to this post.


Top
   
PostPosted: Wed Jul 11, 2018 8:49 am 
Offline

Joined: Sun Dec 18, 2011 10:29 pm
Posts: 21
Moreover: what does the orange cycle mean close the EL6910 module in the project tree while online?

Thanks.

Attachment:
Immagine2.png


You do not have the required permissions to view the files attached to this post.


Top
   
PostPosted: Fri Jul 13, 2018 8:17 am 
Offline

Joined: Sun Dec 18, 2011 10:29 pm
Posts: 21
Hello all,

I consider the issue closed.

For the sake of information, the alarm message comes from wrong connection of safety blocks while le orange circle means missing licence for the lib OdDrvEL6910.


Top
   
PostPosted: Fri Jul 27, 2018 7:23 am 
Offline

Joined: Tue May 16, 2017 7:26 am
Posts: 2
Hi all,

I just found this topic and I'm using the EL6910 for analog values.

I watched the tutorial https://www.youtube.com/watch?v=y5c-ZxtCc0o and I'm surprised that the log. devices (FSOE from safe devices) are automatically be added to the EL6900.

Unfortunately this is not working anymore with the EL6910...

Would be great if this could be integrated again...

Thanks
Stefan


Top
   
PostPosted: Wed Aug 29, 2018 8:11 am 
Offline

Joined: Sun Dec 18, 2011 10:29 pm
Posts: 21
Hello Stefan,

what kind of analog cards do you use?

Thanks.


Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 10 posts ] 

All times are UTC+01:00


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Limited