Author:  BIZON [ Sat Mar 31, 2018 1:49 pm ]
Post subject:  PLC Berghof DC2007 connect via Ethernet/IP

Good day,
I want exchange information between DС2007 https://www.berghof-automation.com/en/products/dialog-controller/resistive/ba-dc-7-r-touch/ and SICK IVC-3D51112 https://www.sick.com/ru/ru/vision/-3d/ivc-3d/ivc-3d51112/p/p148167 via Ethernet/IP.
I have seen this video and try repeat https://www.codesys.com/products/codesys-fieldbus/industrial-ethernet/ethernetip.html

After add Ethernet adapter and Ethernet_IP_scanner, to rpoject device. Load to plc and RUN. Arrow cyclic near Ethernet_IP_Scanner was orange. Near Ethernet -green.
Moreover in video i have seen that in repository device was WAGO and Leuze. Where i can download and add to codesys repository device SICK. Thank you for help.

Author:  Berghof-Support [ Thu Jan 31, 2019 2:15 pm ]
Post subject:  Re: PLC Berghof DC2007 connect via Ethernet/IP

Hello Bizon,

we just recently entered the CODESYS Forum, so even if your
question was asked some time ago, we want to answer you.

The EthernetIP scanner and adapter are comaptibale with the DC2007.
The orange circle you saw indicates that this feature is running in
demo mode (fully featured but with an integrated timer)
which is normal, as you don't have the license installed.
In order to do some testing, and setting up everything
you can just use the demo mode.
This license can be purchased seperately from Berghof.

In order to add your Sick device to the CODESYS repository you,
must go to Sick Homepage and download the correct
hardware description file, and install this file into the CODESYS device repository.