Hello
I've been given an EDS file to talk to a Kawasaki robot controller.
It installs ok, but only Input data seems visible.
If I install it in another Ethernet/IP configurator (Omron) then Input and Output data appears.
Could anyone have a look? (I've changed extension from eds to txt to upload it here)
ph0010421 hat geschrieben:
Hello
If you open up the file, you'll see that the path for Exclusive owner is incorrect with some extra bytes:
"20 04 25 00 00 04 2C 96 2C 64"; $ Path
This should be more like:
"20 04 24 04 2C 96 2C 64"; $ Path
If you use EZ-EDS (https://www.odva.org/software/EZ-EDS-Download), open up the file and go down the Connection Manager -> Connection1 .You won't be able to Create/Decode path. Anyway, I've attached the updated EDS. Let me know how it works.
Hello
Kawasaki E con V1.0.txt [13.16 KiB]
Kawasaki E con V1.0 (2).txt [13.29 KiB]
That's really kind. I'm visiting Kawasaki next week to try and make this work. I'll certainly let you know.
Hi.
Just to let you know this this worked.
I really appreciate your help. Kudos to you for spotting the error.