It is currently Fri Oct 18, 2019 12:06 am
PostPosted: Fri Sep 27, 2013 1:44 pm
Hi all,
Recently I used the Modbus master library (CoDeSys V3.5.3.0).
And I noticed that dis-connecting and re-connecting the serial cable does NOT restart the Modbus protocol.
Do you have any experience with (re-) starting the Modbus protocol?
Is there a way to:
- detect that the Modbus protocol is not running.
- (re-) start the Modbus protocol manually (by the application).
Any help is appreciated.
Regards,
Edwin.
PostPosted: Fri Sep 27, 2013 2:12 pm
Yes, this is known.
In the device tree you can set the name of your slaves (right click => properties).
This name is the instance of your Modbus Slave.
To detect the error and reset the communication you can use e.g. (mbSlave1 is the name of my Modbus slave device):
IF mbSlave1.xError THEN
mbSlave1.xReset := TRUE;
ELSE
mbSlave1.xReset := FALSE;
To get the error message you can use
bySlave1Error: IODRVMODBUS.MB_ErrorCodes;
bySlave1Error := mbSlave1.byModbusError;
PostPosted: Fri Sep 27, 2013 4:49 pm
Tim,
Thank you for your quick answer.
I'll apply it immediately.
Do you know where I can find a list of known issues?
(I do not have access to the CoDeSys jira database.)
Regards,
Edwin.
PostPosted: Sat Sep 28, 2013 5:45 pm
Please contact your supplier for this.
Jira is only accessable for direct customers (OEMs) of 3S-Smart Software Solutions and Distributors.