Edwin Schwellinger wrote:
Hi,
at the moment you are on Control Win, the non realtime capable plc
for this to use Ethercat you need to install WinPcap. Then it will work that way.
If you need realtime capabilities you need to switch the plc to
https://store.codesys.com/codesys-contr ... l?___SID=UControl RTE.
Then no winpcap is needed, you needed then to install the CODESYS network driver in the Windows device Manager and add the component to the RTE configuration.
BR
Edwin
Thank you for support, I installed winPcap but got the same issue then I try to install Npcap and now I can scan and add slave to devices tree and one more thing, the software can not update I/O status as below:
Attachment:
z1629003513124_43b7b2104b50010d45bc164d3d3a9813.jpg
May i use Control win for update I/O status online?
when i run i got 2 error like :
Attachment:
z1629104406365_e2b06c212ac9ed21af1a569511274677.jpg
Please help me if you can.
Thank you again,
Andy