 Post subject: MODBUS TCP Slave
PostPosted: Thu Oct 19, 2017 9:01 am 
Offline

Joined: Mon Oct 16, 2017 1:47 pm
Posts: 1
Hello,
I have Codesys 3.5 patch10 and a Berghof screen.
I want to use Modbus TCP slave device but I don't know how to change the type of variable. Automatically the device sends WORD. Can we send DWORD or REAL?
It's so weird that it's %IW and not %MW... :oops:
Some idea?
Thanks. :D [/color]


Top
   
 Post subject: Re: MODBUS TCP Slave
PostPosted: Tue Oct 31, 2017 10:33 pm 
Offline

Joined: Sat Oct 21, 2017 3:42 am
Posts: 1
Modbus is 16 bit words, you will need to split/combine multiple words on each end of the modbus path to get your DINTs and REALs.


Top
   