MODBUS

thaisjx
2015-06-18
2015-06-22
  • thaisjx - 2015-06-18

    Hi there,

    I'm using a MODBUS configuration in CODESYS between a WAGO 758-874/000-131 and a WAGO 750-872.
    The project compiles with no errors but I can't write in the OUTPUTs of my slave (WAGO 750-872). I only can read its inputs.

    Maybe is there any library missing? Could anybody help me?

    Thank you very much!

     
  • shooter - 2015-06-18

    what addresses are you using on the slave, and what is the configurstion.
    you will need to add an offset for correct addresses.

     
  • thaisjx - 2015-06-22

    The problem was that my outputs were configured in PI allocation as 'PLC, PLC' not as 'Modbus TCP/UDP'. But now it works.
    Anyway thank you for your answer. Have a nice day.

     