I have an IFM CR0032 PLC configured (using CoDeSys v2.3) as a CANopen slave. When the master does an SDO read of 0x100A (SW version) the PLC resets . Bus trace:
I can also verify that a PLC reset takes place because I hear the internal relays clicking. In the CoDeSys project the variable associated with 0x100A is STRING(3) := '24T', read-only. I expect (and have elsewhere seen) a response of a 4-byte, null-terminated string.
Anyone have experience with this? Or have insight into why the PLC reacts this way?
It appears that CANopen for the IFM CR0032 (slave) does not handle SDOs for STRING(n) where n < 4. I verified this on several OD entries. For STRING(n) with n >= 4 an object of 5 or more bytes results, so a segmented SDO is needed rather than expedited. For now this seems to be a reasonable workaround.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Further evidence... create a project using the IFM template for CR0032 CANopen slave. In the Objekt1xxxh PRG change ManufacturerSoftwareVersion to be "STRING(3) := '123';". Run PLC. Read 0x100A via SDO. 5 out of 5 times the PLC resets.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I have an IFM CR0032 PLC configured (using CoDeSys v2.3) as a CANopen slave. When the master does an SDO read of 0x100A (SW version) the PLC resets . Bus trace:
can0 701 [1] 05 // slave heartbeat, operational
<more traffic="">
can0 601 [8] 40 0A 10 00 00 00 00 00 // master initiates read
can0 77E [1] 05 // master heartbeat, operational
can0 701 [1] 00 // slave heartbeat, initialization implies reset</more>
I can also verify that a PLC reset takes place because I hear the internal relays clicking. In the CoDeSys project the variable associated with 0x100A is STRING(3) := '24T', read-only. I expect (and have elsewhere seen) a response of a 4-byte, null-terminated string.
Anyone have experience with this? Or have insight into why the PLC reacts this way?
Related
Talk.ru: 1
Talk.ru: 8
It appears that CANopen for the IFM CR0032 (slave) does not handle SDOs for STRING(n) where n < 4. I verified this on several OD entries. For STRING(n) with n >= 4 an object of 5 or more bytes results, so a segmented SDO is needed rather than expedited. For now this seems to be a reasonable workaround.
Further evidence... create a project using the IFM template for CR0032 CANopen slave. In the Objekt1xxxh PRG change ManufacturerSoftwareVersion to be "STRING(3) := '123';". Run PLC. Read 0x100A via SDO. 5 out of 5 times the PLC resets.