PostPosted: Thu Apr 14, 2016 11:34 pm 
Offline
User avatar

Joined: Wed Jan 13, 2016 10:06 am
Posts: 1
hello,

Just a precision about the opc ua. I use codesys 3.5.8 and rapberry pi.
I test opc ua this day. Just a little program. No global var. Impossible to obtain access to locals variables with opc ua client. The tree of opc ua server -in the client - is small.

The solution requires to check globals variables to obtain the full tree in the opc ua client (UaExpert, OPC UA Dashboard for example ). It's now possible to display variables.

See attachment file for more information

this may be useful to someone ?


You do not have the required permissions to view the files attached to this post.


Top
   
PostPosted: Wed Jul 27, 2016 2:48 pm 
Offline

Joined: Mon Apr 11, 2016 2:29 pm
Posts: 13
Helle PR35,

Great and I have also tested with the KEPServerEX UA Client, Work all great.

I do have a little question, if you have been able to have the Codesys Runtime to sllep for about 10 sec before startup, since the OPC UA Server /port needs do be delays at reboot/startup to have the OPC UA Server Work correct?

Look forward to receive your feedback.

Peter Grote 8)

PR35 wrote:
hello,

Just a precision about the opc ua. I use codesys 3.5.8 and rapberry pi.
I test opc ua this day. Just a little program. No global var. Impossible to obtain access to locals variables with opc ua client. The tree of opc ua server -in the client - is small.

The solution requires to check globals variables to obtain the full tree in the opc ua client (UaExpert, OPC UA Dashboard for example ). It's now possible to display variables.

See attachment file for more information

this may be useful to someone ?


Top
   
PostPosted: Thu Jul 28, 2016 4:53 am 
Offline
Site Admin

Joined: Mon Sep 05, 2005 9:42 am
Posts: 1936
Hi,
beside the recommendation of Peter with the 10s delay (this is still needed)
I would recommend to use Rasperry Pi Package 3.5.9.10 and CODESYS 3.5.9.10 Development System
There are many bugfixes and improvements according OPCUA.

so a sleep 10 or 20 should be added in
/etc/init.d/codesyscontrol

BR
Edwin


You do not have the required permissions to view the files attached to this post.


Top
   
PostPosted: Wed Oct 19, 2016 10:17 am 
Offline

Joined: Mon Apr 11, 2016 2:29 pm
Posts: 13
Hi Edwin,

This really Work for me, thank you and hope all other using OPC UA will be happy in relation to this note.

Have a great day

BR
Peter Grote

Edwin Schwellinger wrote:
Hi,
beside the recommendation of Peter with the 10s delay (this is still needed)
I would recommend to use Rasperry Pi Package 3.5.9.10 and CODESYS 3.5.9.10 Development System
There are many bugfixes and improvements according OPCUA.

so a sleep 10 or 20 should be added in
/etc/init.d/codesyscontrol

BR
Edwin


Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 4 posts ] 

All times are UTC+01:00


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Limited