Welcome to our new forum
All users of the legacy CODESYS Forums, please create a new account at account.codesys.com. But make sure to use the same E-Mail address as in the old Forum. Then your posts will be matched.
Close
there is a simple workaround for your case: add a TRUE contact just after the powerrail.
This will eliminate the necessity of yet unsupported terminator element which exists between powerrail and branch point.
Regards
Roman
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi Guys,
When I export code written in CodeSyS 3.5 SP10, I get the following error:
The Type: "_3S.CoDeSys.NWLObject.BoxTreeTerminator' is not supported.
If I delete the network (Ladder Logic) it exports fine, but defeats the purpose wouldn't you say...lol
Hi Keithang,
can you identify the network that produces this exception?
Please post a screenshot of it here, probably we will found some workaround.
Regards,
Roman
I am seeing the same error message. The shape of the ladder that causes this problem is seen in the attached pdf file.
TestExport Will not export to PLC Open .pdf [126.82 KiB]
Hi Keithang,
there is a simple workaround for your case: add a TRUE contact just after the powerrail.
This will eliminate the necessity of yet unsupported terminator element which exists between powerrail and branch point.
Regards
Roman